Hi guys and girls,

A client is moving their kitchen into another room that currently has a few sockets in it.

The sockets are currently on a ring final circuit that covers every socket in the house.

They've asked me to add sockets for the new kitchen so I am going to run a new kitchen circuit most of which can be done in trunking as it will be behind the units going in.

My question is am I able to replace the faceplates of the old sockets not being used/covered with a blanking plate and use maintenance free wago's inside so the ring for the rest of the house is not affected? (3 sockets I think that will end up behind units)

Thanks in advance
 
Yes if the wagos are rated appropriately. Your proposed solution would not be Maintainence Free so would need reasonable access for future I&T. Why not just remove the S/O’s and crimp and over-sleeve?
 
If they not gonna be accessible I’d crimp and shrink em, trouble with wagos is they don’t class as MF if not in a wago box....not sure about the insure splice but won’t be to hard to check
 
If the new layout allows, I would leave the sockets in place and cut access holes in the rear of the cupboards..... or if the cables come from below, get them out of the wall and use Hager MF boxes ........
 
I would access the cables above these sockets in the ceiling. I would access from below as there's a pretty good chance some plastering must be going on so the small holes you make in the ceiling can be filled. I would then join the cables in a MF wago and leave in the ceiling.

I doubt the old sockets will be in an ideal place behind the new cupboards, also I doubt that the owner will want big holes cut in them simple so he can see a blanking plate in order to create the needed electrical zone. The kitchen fitter will end up just covering them up with the cabinets and then there will be live cables hidden in the walls.
 
If the new layout allows, I would leave the sockets in place and cut access holes in the rear of the cupboards..... or if the cables come from below, get them out of the wall and use Hager MF boxes ........
I'd love to try and explain that to a customer - yes Mam I know your kitchen cost over £20k, but it was easier for us to put the big holes in the back of the units rather than remove the sockets properly.
 
So can i just confirm, if I use a crimp and shrink or inline splice and then put a blanking plate then it will be classed as MF? I don't want to cut holes etc in cupboards the ring main could do with having a few less sockets on it as it is haha.
 
Hi guys and girls,

A client is moving their kitchen into another room that currently has a few sockets in it.

The sockets are currently on a ring final circuit that covers every socket in the house.

They've asked me to add sockets for the new kitchen so I am going to run a new kitchen circuit most of which can be done in trunking as it will be behind the units going in.

My question is am I able to replace the faceplates of the old sockets not being used/covered with a blanking plate and use maintenance free wago's inside so the ring for the rest of the house is not affected? (3 sockets I think that will end up behind units)

Thanks in advance
If you can get access to the leg in and leg out under the floor, I think it' be a better job to cut out the old sockets and link the old legs under the floor in MF boxes.

A row of blanking plates on the wall is going to look ugly and it's only a matter of time until someone removes them and skims over.

Then you'll have live cables in the wall with no obvious route indicators.

Try to go d the legs and do it properly, all in my humble opinion of course.
 
Split ring remove Surplus sockets join back up with wago’s and wago box under cabinets behind plinths ! Just remember to try and leave enough slack to make it easy in the future to check em.
 
Split ring remove Surplus sockets join back up with wago’s and wago box under cabinets behind plinths ! Just remember to try and leave enough slack to make it easy in the future to check em.
Why check them if they are MF?
 
Not all Wago boxes are MF. The box used must be stamped with the MF symbol. The smaller boxes are not. I have no idea why this is the case, but it is.
 
Not seen the small units before, but do they offer cable restraints? This is one of the main factors in a MF connection.

They have the rubber fins on cable entry to hold the cable sheath firm like the larger box, but not the moulded plastic "stalls" that the connectors live inside.
The smaller boxes are a through box with cable entry each of the short ends rather than the one end.
 
They have the rubber fins on cable entry to hold the cable sheath firm like the larger box, but not the moulded plastic "stalls" that the connectors live inside.
The smaller boxes are a through box with cable entry each of the short ends rather than the one end.
For lighting circuits I believe, never used em though....
 
IMAG8398.jpg
 
time you bought the wago box, wagos, earth sleeved the cpc's, closed box with pipe grips, better off paying £4 for the quickwire solution.
 
time you bought the wago box, wagos, earth sleeved the cpc's, closed box with pipe grips, better off paying £4 for the quickwire solution.

Love the quickwire push in system, but I find wagos in boxes better to keep as they are completely flexible in the connection configuration. Quickwire only do one specific job.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Rugby

Thread Information

Title
Removing socket outlets
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
48
Unsolved
--

Advert

Thread statistics

Created
Bobby34,
Last reply from
vjsmarwick,
Replies
48
Views
8,318

Advert

Back
Top