I posted the other day regarding advice on a switceh fuse for when the CU is a distance from the meter.
I've decided on using a 60amp switch fuse which will be fed with 25mm tails. From the switched fuse to the CU, roughly 9-10 meters, I have specced 10mm 2 core SWA and a 16mm earth. The supply is TN-C-S, so have specced the earth to match that of the tails at the meter, rather than the size of the SWA.
Is this the way in which the regs describe sizing if the main earth. or should the earth be sized on the SWA and not the supply tails.
Maybe quite simple to some, but would like other opinions on it
Thanks
I've decided on using a 60amp switch fuse which will be fed with 25mm tails. From the switched fuse to the CU, roughly 9-10 meters, I have specced 10mm 2 core SWA and a 16mm earth. The supply is TN-C-S, so have specced the earth to match that of the tails at the meter, rather than the size of the SWA.
Is this the way in which the regs describe sizing if the main earth. or should the earth be sized on the SWA and not the supply tails.
Maybe quite simple to some, but would like other opinions on it