Firstly i will ask how old are the storage heaters anything pre 1986 should be handled with care as there is a very high probability they contain asbestos or related products ,what sort of tests for a PIR or just maintainance
 
Main fault will really be faulty element, open up the heater, pop on the temp supply and feel to see which ones heat, if none then check the thermal cutout.
 
You would need it connected to supply for that anyway if it does not appear to work look out for something about the size of a penny on that will be a re set switch which may solve the problem. These things are so basic you dont have much to go wrong oh and bring a stubby screwdriver with you or you may not be able to get the cover off.


Chris
 
Isolate the supply at the switch remove front cover , Check continuity of cpc from the DP solator switch , check continuity from the Live to neutral ,then across each element ( normally have to disconnect each element to do this ) insulation tests earth to neutral live to earth but omit the neutral to live as this will give you 0.00 , the resetable thermal cut outs check to see if tripped ,will show open circuit if it has , reset if required , the stat is a difficult one cannot realy be tested ,but if suspect replace if no continuity and the thermal trips are ok check the elements ,to inspect the elements remove inner cover remove bricks check elments for distortion breaks holes etc , normal fault blown element runs cooler than normal as elements are wired in parallel
 
Last edited by a moderator:
ok thanx for all your posts i dont have any to do at the moment but theres a good chance i will have to in the near future .......is there any chance of the eco 7 supply causeing a problem ?
 
if they're in-circuit you can energise contactor and check your readings with the clamp- a simple working test

other simple tests are resistance reading and L-E IR test(through stat and cut-out)
 
depends where you are you can come accross the old time clocks they some times have the wrong time due to power failurer and these are sealed ,they are replacing them for radio link ones now but just a thought
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
testing storage heaters
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
rapidrich,
Last reply from
davelerave,
Replies
17
Views
11,936

Advert

Back
Top