I have been a sparks for 30 odd years ,I did my 3 years at college for my 2361 1&2
I have my 16th and my employer does not trust my work now because I'm not 17th soon to be 18th . I was off work and they called in another sparks . He sorted the problem out and said my work was dangerous.
I had a 32a bracket on 2.5 twe supplying 2 x 16amp toasters , I put an amp meter on them and they were pulling 12 amps each. So I know they were fine.
But because this new sparks said I did not have 17th , I could not do any more electrical work.
I work on commercial site .
Has the regulations changed that much ?.
So it's time to say goodbye to a trade I have loved doing for 30 years and will miss it.
Good luck to all the newbees coming into a brilliant trade and look forward to all the new friends you will make .
 
Not sure what you mean by a 32A bracket?

However I must cringe at the very notion of T&E being used in a commercial setting - that cable is designed for domestic use only.
 
If you mean you supplied a single 2.5 twin and earth via a 32 amp breaker then yes that is dangerous.16amp or 20 amp breaker at a push.And i agree that tw&e cable is not really suitable for commercial use.
 
Not sure what you mean by a 32A bracket?

However I must cringe at the very notion of T&E being used in a commercial setting - that cable is designed for domestic use only.
Think he means breaker and sorry I agree it should not have been on a 32A.
Didn't know BS6004 only designate this cable for domestic use, learn something new everyday.
 
If you mean you supplied a single 2.5 twin and earth via a 32 amp breaker then yes that is dangerous.16amp or 20 amp breaker at a push.And i agree that tw&e cable is not really suitable for commercial use.

You can actually have a 2.5mm conductor in a 32A MCB as long as it is only supplying one single or one double socket. That scenario couldn't be applied here but just mentioning it.
 
You can actually have a 2.5mm conductor in a 32A MCB as long as it is only supplying one single or one double socket. That scenario couldn't be applied here but just mentioning it.
I beg to differ.2.5 cable can take a max of 27 amps if clipped direct.23amps in a wall or 21 amps above a plasterboard ceiling with insulation.Putting a 2.5 on anything bigger than a 20amp breaker would be madness.Personally i would put a 16amp breaker feeding it.If you wish to back up your claim then please quote the relevant BS7671 number.
 
You could have 2.5mm^2 T&E on a 32A breaker if overload protection has been omitted (fixed load). Don't know why you'd do it though. T&E is not strictly for domestic use only, it is used extensively in offices, shops etc. It probably should be though. To me, it depends on the setting, I hate seeing it in commercial kitchens, for example, or factories etc.
 
Not sure what you mean by a 32A bracket?

However I must cringe at the very notion of T&E being used in a commercial setting - that cable is designed for domestic use only.
Sorry I call it commercial as it's 9 buildings not a factory. Yes I hate predict text. 32amp breaker supplying a small 2 way board and 16a mcbs in turn each mcb supplying a toaster.
Sorry for the misunderstanding.
Have the regulations changed that much ?
 
Think the 2.5 on 32amp mcb is referred to a spur off the existing ring final circuit which can feed a single or double socket as the idea is the spurred 2.5mm clipped direct at 27amps can't be overloaded
 
Sorry I call it commercial as it's 9 buildings not a factory. Yes I hate predict text. 32amp breaker supplying a small 2 way board and 16a mcbs in turn each mcb supplying a toaster.
Sorry for the misunderstanding.
Have the regulations changed that much ?

I'd have that submain on 4mm^2 at least.
 
I beg to differ.2.5 cable can take a max of 27 amps if clipped direct.23amps in a wall or 21 amps above a plasterboard ceiling with insulation.Putting a 2.5 on anything bigger than a 20amp breaker would be madness.Personally i would put a 16amp breaker feeding it.If you wish to back up your claim then please quote the relevant BS7671 number.

So spurs are banned in your opinion then ? And it's perfectly acceptable to take a RFC spur from the 32a MCB, only feeding one socket though as HHD rightly stated.
 
Sorry I call it commercial as it's 9 buildings not a factory. Yes I hate predict text. 32amp breaker supplying a small 2 way board and 16a mcbs in turn each mcb supplying a toaster.
Sorry for the misunderstanding.
Have the regulations changed that much ?
No the breaker would be oversized it has nothing to do with recent changes.
 
I get the ring final spur but why are people justifying, creating scenarios pushing this cable size to its limit when in reality they wouldn't do it.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Time to call it a day
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
74

Advert

Thread statistics

Created
Sparkhe,
Last reply from
Andy-1960,
Replies
74
Views
8,053

Advert

Back
Top