Search the forum,

Discuss Touch voltage in the Australia area at ElectriciansForums.net

P

peteelecs

Please could someone explain Touch Voltage to me and do I have to check for it when installing socket outlets and how I go about testing for it
 
The safe touch voltage is deemed to be 50 volts. I disagree i have been cracked by much less. In my humble opinion and that of the people who trained me many moons ago, all voltages should be treat as lethal, i have yet to find a reason to disagree with that statement after more than 30 years.

Cheers............Howard
 
The regs state that touch voltage should not rise above 50V.

You can check by taking a continuity reading between exposed-conductive-parts and extraneous-conductive-parts.

The reading you get multiplied by the current causing the protective device of the circuit to operate in the required time must be ≤ 50V (V = I x R).

For RCD protected circuits this would be 1667Ω (0.03 x 1667 = 50V)
 
Last edited by a moderator:

Reply to Touch voltage in the Australia area at ElectriciansForums.net

Similar Threads

Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
596
i need to purchase a voltage proving unit - i have seen Megger MPU690, Martindale PD690, and Socket and See SP400, and Fluke but difficult to...
Replies
2
Views
448
R
Hi. Can somebody please advice what to do next or should I do anything next or just leave that cable as it is? Just bought the house and found a...
Replies
9
Views
487
Resident
R
Hi all, This may is a little odd and may take some getting your head around but here goes... I measured around half the load current on two DC...
Replies
0
Views
97
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
516

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top