Hi,

I have a three phase switch fuse supplying a 16A socket. In the specification provided it states the following:

Design Current - 16A
Main Protective Device 20A

The circuit is fed from a C20 MCCB at the distribution board.

What size of fuses should I be putting in the switch fuse?

16A or 20A?

Thank you.
 
I agree for a single point socket 16A. But it is suggested 20A can be used although I admit these things in GN1 are not necessarily Regulations.
 
Hi,

I have a three phase switch fuse supplying a 16A socket. In the specification provided it states the following:

Design Current - 16A
Main Protective Device 20A

The circuit is fed from a C20 MCCB at the distribution board.

What size of fuses should I be putting in the switch fuse?

16A or 20A?

Thank you.
Op no mention of cable size, ccc is a main factor.
 
...20A is due to the fact a radial of more than one 16A socket can be employed ... however if the circuit supplies one 16A socket I see no reason to use anything above a 16A protective device.
Agree.
Apologies for my dumb question but why are there additional fuses being spec'd here? Local isolation yes, but it's already got a C20 at the board so shouldn't the question be "do I keep the C20 or go to C16?" :)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
GB

Thread Information

Title
What size Fuses do I require?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
32
Unsolved
--

Advert

Thread statistics

Created
Gavin Millar,
Last reply from
Wilko,
Replies
32
Views
3,869

Advert

Back
Top