Clarifiation please !

I have read somewhere, maybe in BS7671 or on a forum site regulation that states that 16mm meter tails can or should be used on supplies rated at 80amps or under and 25mm tails on supplies rated at 100amps.

I have scoured BS7671 and various forums but cannot find this regulation, have I seen this, does such a regulation exist ?

As the current carrying capacity of a 16mm meter tail Is 87amps it would make sense or is this just common practice

Thanks in advance

TC
 
Clarifiation please !

I have read somewhere, maybe in BS7671 or on a forum site regulation that states that 16mm meter tails can or should be used on supplies rated at 80amps or under and 25mm tails on supplies rated at 100amps.

I have scoured BS7671 and various forums but cannot find this regulation, have I seen this, does such a regulation exist ?

As the current carrying capacity of a 16mm meter tail Is 87amps it would make sense or is this just common practice

Thanks in advance

TC
follow the tables in bs7671 and you cant go wrong.

most people install 25mm simply because usually the fusecarier can only take a max 100amp fuse unless its replaced with a slow blow
 
Clarifiation please !

I have read somewhere, maybe in BS7671 or on a forum site regulation that states that 16mm meter tails can or should be used on supplies rated at 80amps or under and 25mm tails on supplies rated at 100amps.

I have scoured BS7671 and various forums but cannot find this regulation, have I seen this, does such a regulation exist ?

As the current carrying capacity of a 16mm meter tail Is 87amps it would make sense or is this just common practice

Thanks in advance

TC
the only info i have found atm in byb is 16mm copper and 25mm ali is the minimum p133
 
Last edited:
Clarifiation please !

I have read somewhere, maybe in BS7671 or on a forum site regulation that states that 16mm meter tails can or should be used on supplies rated at 80amps or under and 25mm tails on supplies rated at 100amps.

I have scoured BS7671 and various forums but cannot find this regulation, have I seen this, does such a regulation exist ?

As the current carrying capacity of a 16mm meter tail Is 87amps it would make sense or is this just common practice

Thanks in advance

TC

The cable size should be calculated in the same way as all other cable sizes are, though it is safe not to worry about VD at that length.
 
personally id change them to 25mm but your right 16mm is ok for 80amp my tails in my house are 25mm but the dnos are 16mm so when they were changing my meter to one of these smart ones i ask him how come my tails have to be 25 and yours are 16 makes no sence he said we work to different reqs ha ha bull ****
 
personally id change them to 25mm but your right 16mm is ok for 80amp my tails in my house are 25mm but the dnos are 16mm so when they were changing my meter to one of these smart ones i ask him how come my tails have to be 25 and yours are 16 makes no sence he said we work to different reqs ha ha bull ****
not really, we work to bs7671. they dont, they work to a different guide book
 
I agree that if we are being told to upgrade tails, then the meter installers should replace them too.

That said, changing tails should be based on the situation, including length, reference method and potential load.
 
CPR got it ... changing tails are subject to the same calcs and rules as any cable throughout an install and its this that denotes the size... the 25mm is a safeguard as we legally do not have access to the DNO cutout fuse rating and as in most domestic this is inside a 100amp rated carrier then we are to assume it for a max rated fuse.
If you have knowledge of a lower rated fuse then that can be used for your design and thus in your situe be 16mm.
 
The Best Practise Guide for domestic consumer unit change (number 6) says on page 5 (note 4 I think) that you can keep the 16mm tails even if there is a 100A cut out fuse..... as long as it meets reg 434.5.2 (i.e K[SUP]2[/SUP]S[SUP]2[/SUP] is greater than I[SUP]2[/SUP]t) AND your max demand is less then the CCC of the 16mm tails.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
regulation for 80amp fuse and 16mm meter tails
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
topcat72,
Last reply from
davesparks,
Replies
18
Views
40,375

Advert

Back
Top