- Reaction score
- 10,616
1) Would you say 1667ohm between extraneous conductive and exposed conductive is at 'substantially the same potential'?
2) So we are testing to see if supplementary bonding is required in case a piece of pipe work becomes live?
historically (16th) supplementary bonding was fitted for the same reason as main protective bonding to reduce the potential between exposed conductive parts and extraneous conductive parts and not to provide a fault path for the disconnection of the protective device?
cheers
sam
1) Less than 1667, is as far as the regs are concerned, if 30ma RCD is used
2) Supplementary bonding, involves the connecting together the conductive parts of electrical & non electrical items, to prevent the occurrence of a dangerous voltage between them under fault conditions. Testing pipe work (in certain locations), is to see whether its 'Extraneous' or not.