1) Would you say 1667ohm between extraneous conductive and exposed conductive is at 'substantially the same potential'?

2) So we are testing to see if supplementary bonding is required in case a piece of pipe work becomes live?
historically (16th) supplementary bonding was fitted for the same reason as main protective bonding to reduce the potential between exposed conductive parts and extraneous conductive parts and not to provide a fault path for the disconnection of the protective device?

cheers

sam

1) Less than 1667, is as far as the regs are concerned, if 30ma RCD is used

2) Supplementary bonding, involves the connecting together the conductive parts of electrical & non electrical items, to prevent the occurrence of a dangerous voltage between them under fault conditions. Testing pipe work (in certain locations), is to see whether its 'Extraneous' or not.
 
Absolutely not.. Diferent ph levels and salts in water can make it more or less conductive according to levels.. What is stopping the water board putting conductive pipe joint underground and then this becoming extraneous conductive.. Small copper pipe after stop tap earth to MET no PD between earths in installation, tick jobs a good one!

:rolleyes:.....On yer' own fella!
 
Absolutely not.. Diferent ph levels and salts in water can make it more or less conductive according to levels.. What is stopping the water board putting conductive pipe joint underground and then this becoming extraneous conductive.. Small copper pipe after stop tap earth to MET no PD between earths in installation, tick jobs a good one!
I'm a bit confused by your statement. If you have a plastic incoming water service and plastic property pipework, you would install a piece of copper pipe after stop cock and bond that. Then this will earth the water in the plastic pipe? Or have I got that completely wrong.
 
1) Less than 1667, is as far as the regs are concerned, if 30ma RCD is used

2) Supplementary bonding, involves the connecting together the conductive parts of electrical & non electrical items, to prevent the occurrence of a dangerous voltage between them under fault conditions. Testing pipe work (in certain locations), is to see whether its 'Extraneous' or not.

1) i wouldnt say that two metallic parts that are 1666 ohms apart are at substantially the same potential, despite our interpretation of reg 415.2.2

2)Thats what i don't understand; - having 1666 ohms between an exposed conductive part and an extraneous conductive part during fault conditions will give a voltage approaching mains - depending on the circuit impedance of course.

cheers

sam
 
Yes i do.! What do you have against this apart from profit margin, sinks and taps are not plastic even if supplied from plastic pipes! I realise its a bit ott, but if there was ever any change to the supply pipe or if there was a leak external an earth path could exist.! Do you not think water is conductive?
 
Yes i do.! What do you have against this apart from profit margin, sinks and taps are not plastic even if supplied from plastic pipes! I realise its a bit ott, but if there was ever any change to the supply pipe or if there was a leak external an earth path could exist.! Do you not think water is conductive?

Are you getting your water from the atlantic? lol
 
1) i wouldnt say that two metallic parts that are 1666 ohms apart are at substantially the same potential, despite our interpretation of reg 415.2.2

2)Thats what i don't understand; - having 1666 ohms between an exposed conductive part and an extraneous conductive part during fault conditions will give a voltage approaching mains - depending on the circuit impedance of course.

cheers

sam
1) My science is not too good; if the resistance is too high, then the RCD will not operate. If it's very high, then it's unlikely to matter
2) Can't help you there, perhaps someone more intelligent than me, will be able to answer that
 
Last edited:
In reply to #39.

Think we all know that water conducts electricity, that's why we have take extra precautions in special locations. However, my understanding of BS7671, is that we are bonding incoming metal pipes, to prevent them introducing potential. I'm not a scientist, but if in the next edtion of BS 7671, they tell me to bond a plastic water pipe, because the water inside can introduce a potential, then I will.

You should google the subject, here is one such piece of research; http://www.plasticpipesgroup.com/media/1036/earthbonding.pdf
 
Last edited:
In reply to #39.

Think we all know that water conducts electricity, that's why we have take extra precautions in special locations. However, my understanding of BS7671, is that we are bonding incoming metal pipes, to prevent them introducing potential. I'm not a scientist, but if in the next edtion of BS 7671, they tell me to bond a plastic water pipe, because the water inside can introduce a potential, then I will.

You should google the subject, here is one such piece of research; http://www.plasticpipesgroup.com/media/1036/earthbonding.pdf

ok playing devils advocat- why do you earth an installation that is copper pipe for water copper gas, but both incoming gas and water pipes are plastic?
 
I'm loving the image of 6 inches of copper pipe with a bonding clamp on it :) Daz
 
Water is not conductive however any impurities dissolved in it will make it slightly conductive.

Experimentation has proved that a 22mm plastic pipe of 600mm length is enough to provide a fully insulated section between 2 copper pipes due to the resistance of the mass of impure water contained within it.
 
Well im affraid sir your very wrong!

Water is made up of co-valently bonded hydrogen and oxygen atoms with no overall charge so electricity cannot flow through water alone. However that co-valent bond can be broken by a high enough voltage which will release the hydrogen and oxygen atoms in their gaseous form.

The addition of other substances with ionic bonds dissolved in the water results in charged ions being free to move in the water and this electricity can flow although it will have a relatively high resistance.
 
If in doubt then insulation test at 500v from MET to part in question <22k ohms bond if not NO NEED! If an installer wanted to he can nothing in bs7671 to say you cant!

But you may make the installation more dangerous if you bond unnecessarily. Daz
 
Would you care to elaborate on that??

You are effectively making whatever it is that you have bonded a part of the electrical installation. For example, a metal sink - this cannot introduce a potential (even earth potential), and so is not extraneous and should not be bonded. You would not be making things safer by bonding it. Daz
 
1) i wouldnt say that two metallic parts that are 1666 ohms apart are at substantially the same potential, despite our interpretation of reg 415.2.2

2)Thats what i don't understand; - having 1666 ohms between an exposed conductive part and an extraneous conductive part during fault conditions will give a voltage approaching mains - depending on the circuit impedance of course.

cheers

sam

1/ They're not substantially the same Sam. The 1667 is to determine whether bonding is required in the first place. If they were not bonded but the circuits were protected by a 30ma rcd then if the resistance between them was less than 1667 ohms then the touch voltage between the two would be 50v or less, so there would be no requirement to bond.

2/ Not if there's a 30ma rcd, it will trip. If there is no rcd then you do not use 1667, you have to bond regardless.
 

Reply to Whilst we're on the subject of bonding... in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top