Currently reading:
Shower circuit on living room ring (Customer only want CU changed)
Discuss Shower circuit on living room ring (Customer only want CU changed) in the UK Electrical Forum area at ElectriciansForums.net
robo83
Hi,
I visited a property today and after initial checks and before i go ahead with the quote i noticed that the shower (power shower) is supplied from the living room Ring.
I've informed the customer that this is not to regulations and requires its own supply. At the moment the customer doesn't want the new circuit installed for the shower and is expecting only a CU change.
How would you go about this and what actions would you take?
Regards,
Robo
My apologies for not replying sooner and incorrect information, i posted just before poping out.
The shower is an electrically heated shower, 7.2kw. At the moment no issues as there is minimal load on the rest of the ring.
Is it on a 32A ring?
7.2kw is about 31A. They must have very little else plugged in at the time the showers running.
Having said that, cables and protective devices can cope with much higher ratings than the max listed. How longs an average shower? 6-8mins??
You need to stress to the client, that the shower circuit needs to be wired in the correct size cable and own radial,before any CU change, either he agrees to disconnecting the shower if no remedial allowed, otherwise walk away.
There is only a TV and a few low voltage lights on the rest of the circuit.
Thanks for this advice, this was the opinion i was taking and going to let them know tomorrow.
My apologies again for the bad explanation on the first post, my focus of the thread was dealing with the customer. My opinion was of walking away, i have had very little dealings with domestic clients and mainly commercial.
so do electrically pumped showers generally use less power than a electrically heated shower?
With respect, that is worrying that you need to ask that when you are quoting for corrective works in someone's home. Also, there is issues with loading 7Kw from a single point of the ring, which from your other post, you don't see as an issue either. Genuinely, you should leave this one until you have more experience (which you will get), it is not being fair to the client mate.
He is not the op.?
with respect you should have gone to spec savers
Reply to Shower circuit on living room ring (Customer only want CU changed) in the UK Electrical Forum area at ElectriciansForums.net