OP
hightower
Why should they be different though?They are for earthing not bonding.
Discuss Bit quick advice please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Because for a cpc the Adiabatic equation can also be used.Thanks but why are they different. Why is a steel to copper equivalency that's good for a CPC not good enough for bonding?
544.1.1 and the * under table 54.8 both say about the bonding conductor being copper or a cross-sectional area affording equivilant conductance in other metals. GN8 has a section on it but I don't have it around me ATM. Probably to do with limiting touch voltages under fault conditions etc.Why should they be different though?
Man did I struggle with this one ... The SWA table gives k numbers suitable for use in the adiabatic equation. I haven't got it open, but I recall the factor is about 2.2. For bonding it's about voltage rise so it's the resistivity that's important and as LSK has said the factor is about 8.5. So armour is normally ok for CPC but rarely enough for bonding.Why should they be different though?
So what are the copper equivalent columns in that link referring to then? Reason we've used 4-core is because it's what the factory owner had lying around and he's on a cost saving exercise. Will have to have a look at pulling in a separate conductor.
Cheers guys. I've just had a read of the relevant section of GN8 but it didn't offer any reasoning behind the 8.5 factor and the difference between a CPC and bonding conductor in terms of copper equivalency.
Theres an echo in here .......They are for situations where you need to know the copper equivalent CSA, this is not used for bonding.
For bonding you need equivalent conductance, this is a different physical property. A factor of 8.5 is generally accepted as being the ratio of conductance of copper versus steel. So for a 10mm copper bond you need 85mm steel.
Or rather raise the temp of the armour I should sayGn8 also gives warning to using the armour as a combined cpc/protective conductor as with tncs diverted neutral currents can raise the temperature of the cable meaning a increased sized conductors maybe needed for your ccc.
It's up to the designer whether this may happen or not.
Reply to Bit quick advice please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net