Someone has asked for an upgrade to their consumer unit but they have no water bonding. I explained this and said it needs to be done but it's quite a job and they don't want it done, just the CU upgraded?
What's the crack with that?
Can you crack on and put it down as a departure from bs7671?
Or walk away, safety should have no cost if they wont pay walk away.
So the IET come out with regs, make no attempt to publicise the regs and leaves the poor sparks to educate the public.
This is not acceptable.
So, our responsibility is to make sites safer and, as such, updating a cu to one with. MCB's and RCD's is making the site safer.
Tin hat on
Just saying..
Ps. None of the CPS make any attempt, that I am aware of to educate Joe public either.
My advice to the op is to provide a written quote with the cu and bonding update ... Then see what happens.....
Thanks everyone, just a situation I have not yet come across.
Can anyone give me an example of when you might use the departures section? Just out of interest really. Again, never used it or seen it used!
sometimes you canfind a cold water pipe in an easier location to bond. in that case, it could be noted as a departure, as long as a R2 test confirmed that said bond had an acceptable resistance to the pipe where you'd have liked to bond ( i.e. close to the point of entry ).i done that with the gas here. as the main gas pipe passess next to the CU. the entry point is 10yards away in the attached garage.
Reg 528.3.4
ii) Fault protection shall be afforded in accordance with the requirements of section 411.
If I'm completely off target, please feel free to tell me, I'm here to learn. As far as I'm aware, if you can't guarantee you electrical services, are not in close proximity with other services, section 411 applies?
Reg 528.3.4
Yes but that's nothing to do with main protective bonding of extraneous parts :mtongue::) although it is part of ADS
Chapter 54 deals with protective bonding
Reply to New CU but no water bonding... in the UK Electrical Forum area at ElectriciansForums.net