Discuss A new type of ring circuit??? in the UK Electrical Forum area at ElectriciansForums.net
Thanks Dale makes sense, what if you can't find the break or a j/b somewhere or only broken on say one leg ?if the ring has no continuity end to end then it is already split, or partially split. If your only option for rectifying this is to make it two radial circuits then you have to disconnect at the two sockets which are on either side of the fault.
Thanks makes sense, meant if say the brake is only on one conductor ie the phase or neutral or even the cpc, but yes understand thanks for taking the time to explain ?My post was what you can do if you cant find the break. If you can find the break then you can fix it.
You will have identfied which two sockets the break is between, if you then cannot find the break then you can disconnect the faulty section of cable from both of the sockets that the break is between and you will be left with two radials.
if you cant find which two sockets the break is between then you aren't yet competent to be doing the work unsupervised as it shows a significant lack of basic skills.
What do you mean by only broken on one leg? 'leg' is not a defined term as far as ring circuits are concerned so can mean different things, you need to be a bit more specific.
Ohhhh yes, completely forgot about that, thanks for the nudge. So I didn't want too much mission creep so did not go to far into it. Have a look at the pic see what you think.what did you find on inspection @Vortigern ?
Maybe it should just say RING CIRCUITS.....even allowing for the breaker ratings.View attachment 60294
About to embark on wiring an extension and cursory examination threw up the above. Have not as yet poked inside. Anyone seen this arrangement before? Can I believe what my eyes seem to be saying to me?
Looks like smoke to me.Ohhhh yes, completely forgot about that, thanks for the nudge. So I didn't want too much mission creep so did not go to far into it. Have a look at the pic see what you think.View attachment 60417
Bear in mind it is cct 4 and 5. I am working on extending cct 3 and don't want to get into mission creep. The fluff has been removed since. It is some kind of cavity filling blown in through the back of the CU. So looking at it I am none the wiser, bit of a mystery eh! Client is a "private" kind of person and has a dog which must apparently be kept from men as it hates men, a rescue dog. So wife and dog are heard and not seen lurking in the bowels of the house. I have not been allowed past the kitchen and tradesmens' entrance. Suppose I can only advise them to have it investigated, but then again is it necessary.
Reply to A new type of ring circuit??? in the UK Electrical Forum area at ElectriciansForums.net