Hello, I’m trying to change a pendent light, I’ve wired it the same as the previous light that was on there however the light is now permanently on and the switch does not work, there are two line wires tied together, two neutrals and an earth wire. I took off the new pendent light and I wired up the previous light the same as it was before (line to line and neutral to neutral with one neutral into a wago connection hanging freely) and that is now staying permanently on. what is it I’m doing wrong?

Thank you for any advice.
 
It's definitely not wired as before.

Can you provide an image of the wiring?
Thanks for your reply, I’ve wired line to line and tried switching both neutrals around but yeah you’re probably right, I’ll attach a photo of the wiring going to the pendant, I’m not sure which wire comes from the fuse box and which wire comes from the switch.IMG_2680.jpeg
 
one of those blue wires is likely the N
the other is likely the switched live.
however it cant be ascertained which is which without some testing.
also the connector blocks shown in the picture are not suitable to be shoved through the hole in the ceiling so the new light fitting fits.
if you know anybody in the electrical trade, this is a great one to offer a beer to compensate for a few minutes work.
at least it will be safe and marked up correctly for anyone else that follows.
 
  • Like
Reactions: nicebutdim
This is the wiring as it was?

I gather you connected the two lives to the live terminal and this is most likely to be why the light is on permanently.

Only one of those blue wires will be neutral and the other a switched live.
 
  • Like
  • Agree
Reactions: DPG and westward10
Agree with @nicebutdim and the evidence is "neutral into Wago connection hanging free".
 
This is the wiring as it was?

I gather you connected the two lives to the live terminal and this is most likely to be why the light is on permanently.

Only one of those blue wires will be neutral and the other a switched live.
Yes, they were already tied together and connected up to the live wire of the pendent light and one of the neutral wires connected up to the neutral wire of the pendant light. Are you able to advise how it should be connected up? Would be appreciated. I have the two live wires, one neutral and one switch live and two earths. On the pendant there is a live, a neutral and an earth. Thank you.
 
And I agree with James that this is definitely not a suitable way to terminate cables in a ceiling void.

The rose which has been removed acted as a junction for the pendant which hung below. These terminations need to be suitably enclosed and consideration given to earthing requirements of the replacement light fitting.
 
  • Like
Reactions: James
one of those blue wires is likely the N
the other is likely the switched live.
however it cant be ascertained which is which without some testing.
also the connector blocks shown in the picture are not suitable to be shoved through the hole in the ceiling so the new light fitting fits.
if you know anybody in the electrical trade, this is a great one to offer a beer to compensate for a few minutes work.
at least it will be safe and marked up correctly for anyone else that follows.
Thank you, I may have to if I’m not able to sort it myself. Thanks for your reply.
 
  • Like
Reactions: DPG
Yes, they were already tied together and connected up to the live wire of the pendent light and one of the neutral wires connected up to the neutral wire of the pendant light. Are you able to advise how it should be connected up? Would be appreciated. I have the two live wires, one neutral and one switch live and two earths. On the pendant there is a live, a neutral and an earth. Thank you.

The browns will have been connected together in the central terminal of the rose, but they definitely weren't connected to the live going out to the pendant (if all information in opening post is correct).
 
And I agree with James that this is definitely not a suitable way to terminate cables in a ceiling void.

The rose which has been removed acted as a junction for the pendant which hung below. These terminations need to be suitably enclosed and consideration given to earthing requirements of the replacement light fitting.
How should I enclose them correctly?
 
Again assuming all information in opening post is correct; the two browns remain connected together, but not to anything else.

One blue is neutral and must be connected to neutral terminal of light fitting. The other is switched live (it should be identifed as such) and is connected to live terminal of light fitting.

There is no way of telling which is which without some basic testing being carried out.
 
The browns will have been connected together in the central terminal of the rose, but they definitely weren't connected to the live going out to the pendant (if all information in opening post is correct).
Sorry, just saw your post.
 
Again assuming all information in opening post is correct; the two browns remain connected together, but not to anything else.

One blue is neutral and must be connected to neutral terminal of light fitting. The other is switched live (it should be identifed as such) and is connected to live terminal of light fitting.

There is no way of telling which is which without some basic testing being carried out.
Thank you for your help
 
  • Like
Reactions: DPG
So I should connect the switch live to the love of the pendant correct?

We don't know which is the switched live. Trial and error isn't a suitable method of testing. I would advise, as other have, that you get an electrician in. They'll be able to quickly determine which wire is which and place the terminations in a suitable enclosure.
 
  • Like
Reactions: R62538472
We don't know which is the switched live. Trial and error isn't a suitable method of testing. I would advise, as other have, that you get an electrician in. They'll be able to quickly determine which wire is which and place the terminations in a suitable enclosure.
Ok, I’ll do that, thank you for your help again, could you tell me what I should put the wires in to instead of them wagos? Thanks.
 
  • Like
Reactions: nicebutdim
Wagos aren't the issue.
I meant to terminate the loose ones, the other person who replied advised I shouldn’t be using them in a ceiling void. Is that correct?
 
I meant to terminate the loose ones, the other person who replied advised I shouldn’t be using them in a ceiling void. Is that correct?

No connections with exposed basic cable insulation should be left in a ceiling void.
 
Can you show the connection parts of the new light.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Help need wiring a light
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
27

Thread Tags

Advert

Thread statistics

Created
R62538472,
Last reply from
R62538472,
Replies
27
Views
2,980

Advert