I've come across a job where the emergency bulk head is wired direct to the CU, but it isn't lighting up, however if you trip the MCB, then the emergency back up kicks in and it is lighting, anyone come across this before?

Cheers Jools
 
with the MCB closed, check if you have 240V at the fitting. i assume you have as the battery back up is held off. once this is confirmed, i think you'll find the fault is in the fitting itself. btw, welcome to the asylum. if it's a non-maintained set up, though, then it's working as it should. i.e. no light until the power is dropped off.
 
thinking about it, it's probably non-maintained and thus perfectly OK. that means that the 240V supply is only to keep the battery charged, not to illuminate the fitting.
 
check with the client to find out if the fitting is normally on or off. usually there is a link across 2 terminals that you fit in order to maintain the light on when power is present.
 
I've come across a job where
the emergency bulk head is wired direct to the CU,
but it isn't lighting up, however if you trip the MCB, then the emergency back up kicks in and it is lighting, anyone come across this before?

Cheers Jools

are you saying this emergency light is on its own circuit? if so, how will it come on in the event of a lighting circuit failure?
 
probably a case of just fitting the link to make it maintained. check with manufacturer as to where the link goes. usually between the Lin and an adjacent terminal.
 
The client says that, the fire brigade told her that it has to be lit at all times, there is another switched light in the area, so this seems a bit OTT.

depends on the environment. if it's an office with plenty of lights and everyone knows the lay of the land, i would say non maintained is fine.
 
The CU is a twin RCD board, when one RCD trips, then the emergency light comes on, never seen electrics like this place before.

yes, the rcd will isolate all the circuits that it is protecting. but, if your lights are on mcb '1' and, the em' light is on mcb '2', the emergency light won't be activated when mcb '1' is tripped.
 
@ jools. the em's should be fed from the same circuit as the local lights, so that if the supply to those local lights fails, the em will light up.
 
once worked there for a few weeks on a sports store ( like jjb, but called something else). parked van as close as possible, about 200 yards from site, and this jobsworth threatened to have the bomb squad blow it up as it was close to a bus station. FFS. as if al quada are going to blow up buses in middleton.
 
I'm working in Middleton


Hope you've got a big dog sat in the van whilst your working lol. Better train it to put car/van fire out as well pmsl.


Yes Tel it is that bad as you have seen. Not all of that area but on some streets even the police dont walk by themselves.
 
It isn't THAT bad

It used to be. Mind you I was brought/dragged up on Ebor Gardens estate so Miggy is'nt that bad really. I play golf at Miggy but never through the school summer holidays. Got sick of the teenage chavs on their motorbikes riding on the fairways. few years ago a nicked 4x4 car did donuts on some of the greens.

Anyway have you sorted out this em light yet?
 
middleton village is alright.

just stay out of belle isle.

Yep the village is nice (one of our members live there)

NOW with a user name of "shagbite" and you know a lot about Belle Isle, can I put two & two together and make 26? Painting a mental picture right now of you lol. (no offence ment mate)
 
so the em' light needs to be linked across to the lighting circuit?

jools, if i was doing this job, i'd just put both radials into one breaker - providing i wasn't overloading the circuit. this, by definition, then becomes one circuit.

when testing zs, i'd take a reading from each leg and use the highest one.
 
SB thats good thinking as the op says its only one EM light and you are allowed to spur off the mcb for one piece of equipment so do it that way, no need to rewire near the fittings.
 
Going back tomorrow to finish off, hopefully, I told client I needed to get advice, there are four radial lights, 2 to each rcd. Shop lights are on same circuit as back room lights. Need to find out when I can go in when the shop is shut so I can safely isolate the CU to work safe, then I can seperate the circuits and make sure it's working correctly. I haven't even taken the cover off of the CU yet, i'm assuming the CU is labelled correctly. But i've made that mistake before
 

Reply to Hello All, need a little advice in the The Welcome Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock