Good Morning
Visited a property yesterday. Customer saying only certain appliances working from double socket in bedroom. Electric toothbrush yes, vacuum cleaner no.
After inspecting socket and wiring find that the socket has been taken as a spur from downstairs lighting circuit on 6A MCB. Circuit tests indicate the circuit itself is okay. Double socket removed and blank plate fitted.
I am thinking that volt drop is the reason the vacuum cleaner did not work but lower power devices still did. Is this correct?
Many thanks in advance
Sorry I may have miss read your thread, the socket has been spurred from a lighting circuit so you have removed the socket and blanked it off, and you say the circuit's OK, you need to remove the leg feeding the socket in it's entirety for the circuit to be OK.
Does he need to remove wiring? Someone could install a 5A socket in future for a lamp.
If the circuit was all OK and correctly wired then you would probably find that you could do the vacuuming from that socket (whilst pushing the limits of the MCB).
The likely explanation for a the results you found could indeed be volt drop but only because there was a high resistance joint /loose connection somewhere in the circuit, then when a higher current was drawn the resistance would drop a greater proportion of the voltage and prevent a motor from working. Alternatively a loose connection may allow a low current but spark away the slight contact when drawing a higher current.
Good Morning
No, not volt drop but possibly an extremely loose connection perhaps? Assuming the vacuum cleaner etc does not trip the 6A MCB.
Edit: Ignore - RB posted while I was typing
This is now being overanalysed. A Henry Hoover will trip a 6A MCB with the inrush current when it starts. Try running one of a pendant :)
Well I don't know about you Meggerman, but the chances of that happening are, IMHO pretty slim, better be safe than sorry, remove the wiring.
I wired a radial in upstairs in my house, didnt have any 20A to hand so stuck a 6A on it temporarily, the mrs then plugged the hoover in and it tripped it, more than likely overloaded it, as I would imagine most hoovers probably draw 10A+ possibly.
Someone my parents know in northampton with approx your qualifications and called Pete, must be another Pete. I'm a northampton person myself, well lived there for 28 years them moved to leicester with the mrs as she had a house etc.
Whereabouts do you live?
Pete999
Thank you for replying. I should have said the results of the circuit tests were okay not the circuit itself. I put a terminal block on the legs and wired the cpc to the metal backbox. I put a blanking plate over the backbox and explained to the householder why/what I had done as a temporary fix. I need to follow up today/tomorrow.