upon removing a 230-12v 600va transformer from a large chandelier type light fitting (40x20w bulbs) and seeing the large, around 10mm cables from the secondary side of the transformer this got me thinking - if the is running at full capacity (600va) the current output on the secondary side would be around 50amps.

Now I know that the energy cunsumption at the 230 side is around 800w (just over 3 amps) but surely not really safe to have 50amls potentially in these fittings, particularly when the earth leads at these are 1mm at most?
 
It is not usual for one leg of the secondary of the transformer earthed, therefore the secondary has no reference to earth, in the event of a fault of one leg of the transformer to earth on the secondary side nothing will happen.
 
QUOTE [but surely not really safe to have 50amls potentially in these fittings,]

which fittings ?
The full current is NOT in all fittings anyway
need more info ?
please elaborate !
 

Reply to 230-12v 600va transformer in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top