I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

IMG_5741.JPG


Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

IMG_5742.JPG


Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
 
  • Like
Reactions: Marvo
Seems like a lot of work for a problem that doesn't / shouldn't exist.

The only time I've had that issue is when refitting very cheap sockets where there isn't really enough space for the 3 wires or they have been cut too short and my fat paws won't fit.
 
  • Like
Reactions: suffolkspark
It does mean less risk of things being disturbed when the socket is wraggled on to the back box. And the stranded singles will make things easier. As above though, quite a bit off faffing.

Be interesting to see what people think.
 
Aren't you technically taking two spurs from one point of the ring though?

IE you have ring in and out, plus the third to your spur - but then the socket its behind is also a spur - as the point of junction is now the wagos rather than the socket faceplate
 
I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

View attachment 109255

Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

View attachment 109256

Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
Why not just use the

MK LOGIC RAPID FIX

 
  • Like
Reactions: lozarus
Aren't you technically taking two spurs from one point of the ring though?

IE you have ring in and out, plus the third to your spur - but then the socket its behind is also a spur - as the point of junction is now the wagos rather than the socket faceplate
I agree, he's turned the existing socket into a spur.
 
Effectively picture #2 is what they do in America / Canada called PIG TAILING , they do it a lot over there using Wire Nuts to bind all the cores together in the back of the box and just take a single cable to the socket or as they call it the receptacle.
Most sockets will take 3 x 2.5 cores , except for the really cheap carp ones
 
  • Like
Reactions: mainline
never had an issue before... not with new, clean solid core. As you tighten the terminal screw, the cores will turn so the screw is gripping two cores, and the other is pressed into the back of the hole.
Never twist together.

stand by for other manufacturers following MK..... Still not used one yet, but i can see it being a time saver if fitting out an entire house.
 
  • Like
Reactions: DPG and mainline
I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

View attachment 109255

Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

View attachment 109256

Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
Will you be going back to the jobs to correct them ?
 
  • Like
Reactions: suffolkspark
I believe MK are about to start selling a level connection fused Spur and light witch range later this year
 
  • Like
Reactions: DPG
Ferrules on 7 stranded cable? I’m assuming that’s 6491X?

Or is it fine stranded?
 
  • Like
Reactions: nicebutdim
I believe MK are about to start selling a level connection fused Spur and light witch range later this year
thats useful.... so you know they're straight and horizontal.....

Lever... you meant lever..
 
  • Like
  • Funny
Reactions: pirate and DPG
Personally, I'm in favour of a light witch. Those heavy witches really bug me...
 
I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

View attachment 109255

Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

View attachment 109256

Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
Ridiculous in my honest opinion
 
Personally, I'm in favour of a light witch. Those heavy witches really bug me...
Yeah, it must be hell for the broomstick carrying the heavy ones.
 
  • Like
Reactions: loz2754
Never noticed the ferrules. Can't imagine this being anything other than 6491.

Guess we have to wait for the OP to tell us.
He's probably busy at the moment with his pocket full of Wagos :).
 
  • Optimistic
Reactions: suffolkspark
Will you be going back to the jobs to correct them ?
Why would he go back and correct them, yes its a technical breach of the regs but there's nothing dangerous in what he's done, its still the same number of sockets in the circuit its just that the joint is in the wago and not the socket, those wagos can withstand about 100 amps before they melt according to several video's I've watched on them. I would only ever go back to a job if I realised I'd done something dangerous.

Saying that, its well over the top, those wagos are about 20p each, a pack of ferules, cable ties, 3 coils of conduit cable, might as well not bother doing the job at all. I don't get why people end up with spurs on new wiring anyway, I work with someone who always manages to do this, there is always a socket somewhere that has 3 cables at it on one of his re-wires, it cant be that hard to go in a circle can it
 
  • Like
Reactions: nicebutdim
Pig tailing / splicing / the cables in the back of the box like this using Wagos really isn't an issue as long at the linking single cable is 2.5 or bigger and the OCPD is 32amps or lower.
Wagos are pretty much bomb proof and would run 30amps all day long without so much as breaking a sweat
 
  • Agree
Reactions: timhoward

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Mark42

Patron
~
Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?