I vaguely remember a thread in which someone said they had removed the grey outer on twin and earth, so they could run the line and neutral as singles in conduit.

I also vaguely remember Davesparks (missed member!) explaining why this wasn't OK, but I can't remember why?

Are singles (designed to go in conduit) the same as the conductors in twin and earth (with grey outer removed)?
 
Singles (6491X) have a slightly tougher (possibly thicker?) insulation and is designed to be dragged through conduit without any serious wear and tear…. Metal conduit originally.

Stripped t&e just isn’t the same
Thanks for that littlespark. Just the ammo I needed for an over zealous customer!
 
I do remember something along those lines as I did it in France, stripping UK T&E and using the L&N in plastic corrugated conduit, I was admonished by Dave Sparks just before he disappeared the last time, it was over four years ago, perhaps it is that thread you remember?
 
I do remember something along those lines as I did it in France, stripping UK T&E and using the L&N in plastic corrugated conduit, I was admonished by Dave Sparks just before he disappeared the last time, it was over four years ago, perhaps it is that thread you remember?
Sounds like the one.
Didn't realise it was you that got told off :D
It's a shame he's gone, I valued his knowledge, and I liked his no nonsense style.
 
I remember that more recent one too, but just can’t find it.

Was it possibly Lucien that explained the differences?


Anyway, it shouldn’t be done. Can’t make singles out of the inner cores of a sheathed cable.
 
I remember that more recent one too, but just can’t find it.

Was it possibly Lucien that explained the differences?


Anyway, it shouldn’t be done. Can’t make singles out of the inner cores of a sheathed cable.
Lucien may well have contributed, but it was gruff, accurate reply of Davesparks I remember.
 
Both T&E (6242Y) and PVC singles (6491X) are manufactured to BS6004 so insulation wise they should be no different. The Uo/U are however different with 62624Y being 300/500 and 6491X being 450/750.
That's interesting.
How can one be able to handle higher voltage, if the (inner) insulation is identical?

Is it because the 6242y is within a grey outer casing. I say that, because that would be the only difference.

An example is H05RN vs H07RN.
The latter is designed for up to 700V and has thicker insulation.

Edit... Just done a little research.
6491x is BS EN 50525-2-31, so perhaps the insulation is thicker as its to a different BS than 6004.
 
Last edited:
No idea but 300/500 is generally for domestic use but the rating suggests it can be utilised outside of domestic. The sheath is not relevant because at an accessory or distribution board it is removed. 300v is Uo the voltage between the conductor and earth or bare exposed conductive parts, 500v is U and is between conductors which effectively have double the insulation.
 
As I tried to get across to DS using the UK Regulations and BS against something being used in another country may change the circumstance's, Lucian I remember agreed with me by PM.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Are singles the same as the conductors within twin and earth, just with the grey outer removed?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Mike Johnson,
Replies
12
Views
671

Advert

Back
Top