I am pricing a job to wire 21 new pitches for a caravan park. There will be a meter box beside each caravan with a 16a trip. I will split it into the 3 phases, so 7 caravans per phase.

Im just trying to figure out how to calculate the cable size. Is it better to run a ring main to pick up 7 caravans? If so how do I do a cable size calculation for ring main?

Cheers
 
a 10.0mm SWA radial for 7 pitches will be adequate . probably even a 6.0mm, considering diversity.
 
You could do anything from installing a feeder pillar centrally with a seperate radial to each pitch up to running a large 3 phase cable with a Y joint to tap off a phase for each pitch.

The physical layout of the site and distances involved may have an influence on what the most economical way is.
 
It is something we have done on a few occasions best way is each on there own feed
Fed via a dp 100ma time delay rcd for each circuit
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Belfast
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Caravan site, cable size
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Nicky Murtagh,
Last reply from
Yozza19,
Replies
4
Views
3,647

Advert

Back
Top