Gardner
Would anything forbid me from combining the clothes washer socket and kitchen dishwasher to a single circuit & MCB?
Discuss Combining circuits in the UK Electrical Forum area at ElectriciansForums.net
If you don't have a ring circuit in the area, then preferably 2 X 2.5mm circuits each on a 16A MCB, or a single 4mm radial on a 25A MCB to supply both appliances via socket outlets or FCU's... You'll not go far wrong using either method.
Those that keep going on about NFPA 70 (NEC), THE OP's company supply Portable type cabins to the UK, so the electrical installation to these cabins needs to comply to BS7671...
But where rings are not present, what would be typical? Or would a 32 amp 6mm2 radial take over as long as nothing is hard wired? No, A 32A 4mm radial could be used in place of a say a ring circuit, so long as all other circuit criteria is considered. My suggestion above, was basically solving your problem of connecting two fixed appliances of 2KW or over...
Ok, never mine I see Engineer's response.
So it boils down to this:
Fused sockets means many appliances can be combined.
No, the plug top fuses as well as the fuses in FCU are there to protect the leads/cords connected to the plug top/FCU, NOT the appliance itself. Any circuit must be designed to be suitable for the load it is expected to carry.
I think the ''terminology'' as in ''combined'' is getting confused here, Running two cables (radial) from a single MCB/OCPD is not considered as being suitable or good practice. There is not a problem supplying two or more fixed appliances on a given or dedicated circuit that has been adequately designed to carry the total expected load. You need to distinguish between general socket outlet provision, and a dedicated provision for fixed or multiple fixed appliances of 2KW and over. Something along the lines mentioned in your own NEC...
If direct wired I can not go over 16 amps or what ever the manufacturer states?
Direct wired in the UK generally means connection via an FCU (fused connection unit) for fixed appliances loads up to 3KW. Loads higher than 3KW, then a suitably sized OCPD in the DB is used...