Currently reading:
Do these internally exposed meter tails require mechanical protection?
Discuss Do these internally exposed meter tails require mechanical protection? in the UK Electrical Forum area at ElectriciansForums.net
Hi,
I was hoping someone with a little more insight might be able to shed some light on a potential issue I have, as I can't seem to find another example online where this specific question that has been answered.
What you can see in the attached photograph is meter tails (single insulated + sheathed), coming in to supply an EV distribution board. It seems from research that most installations are buried with additional conduits for protection, so I'm not sure what the specific rules are around clipped-direct meter tails.
The regs are a little hazy, but should these tails, being situated in a garage workshop, in close proximity to daily tool usage and storage, have further mechanical protection, in the form of metal conduit, or is this perfectly reasonable for a new install?
Many thanks in advance,
Drew
Between an OCPD tripping in the original CU as opposed to the new one.
He's got a 40amp in the LV and a proposed 63amp in the main cu.
There is partial selectivity between two MCBs up to the selectivity
limit current if the downstream MCB has a lower rated current than
the upstream MCB
It's a better alternative to having those tails running up the wall.
The surface installation of tails complies with the regulations but disregarding selectivity does not.
And selectivity between what ?
Between protective devices, the 63A mcb will not achieve any selectivity with the downstream MCB's.
the upstream MCB
That's not enough to give much selectivity though. Probably better in this case to split the tails as they have done in this case.
That's not true, there is partial selectivity if the downstream MCB has a lower rated current than the upstream MCB
There are already rcbos downstream of the 40 amp MCB, so does that mean there is no selectivity ?? Even using tails ?
Not true.
Also bear in mind that these boards are next to each other.
How about something like this with the outbuildings MCB omitted.
73 posts on this?
FFS, if you don't like how it looks, cover it up!
Or design it properly in the beginning.
Reply to Do these internally exposed meter tails require mechanical protection? in the UK Electrical Forum area at ElectriciansForums.net
