When conducting an EICR you are inspecting and testing the fixed wiring, power consuming items, such as hand driers etc are NOT part of the fixed wiring, to put it in perspective would you ISITEE (PATest) during an EICR? answer not unless you have charged the client for testing these items, it's a separate job to be priced separately. Unless these tests are in the price for the EICR I can visualise the EICR being very time consuming, more than you would normally expect. The need to document all these items would add hours to an EICR.No, however I'm interested to what members do on here as I've always taken the view that portable appliances with a plug was tested with a PAT tester and fixed appliances was part of the electrical installation and done on the EICR.
Refer to part 5 of the CoP for types of equipment, the equipment does not need to be plugged in to be tested, I would suggest to those in doubt read the CoP and inwardly digest.The problem is caused almost entirely by the term 'PAT testing'. a) much of it is inspection rather than test, and b) it's not just plug-in portable equipment that needs to be tested (fridges aren't portable for instance, but need inspection/test).
As Pete says above, the correct term is ISITEE, and is governed by the code of practice. All is explained in there (well mostly all - it does leave a few things open).
Some hotels put hairdriers, trouser presses etc. on FCUs, but they are not part of the fixed wiring as such, and they need testing (or inspecting, as appropriate).
The deciding factor is not whether the item has a plug on or not.
I wish the term 'PAT test' had never been invented - I spend much time explaining things to people because of this!
The ISITEE is not a statutory document but those listed in #8 are and how you comply may lead you to this CoP.
Oh and apparently if your testing a microwave oven you are supposed to also have microwave leakage detector and test this too , something else we as a company overlookedRead through the link in one of above threads , code of practise for in service inspection and testing of electrical equipment
It would involve disconnecting in spur say and test with adapter to you pat test machine , that way it gets stored with all your other equipments information if you have an advanced pat tester
Or old school , ins res test and earth cont , visual , but keep records of tests , model test sheets are in the book
Basically a real ball ache , something we are avoiding , keeps you in work I suppose
Most company’s now a days will probably state you work to these codes of practises , ours does a long list in our electrical group rulesNot statutory, but highly recommended to use it for guidance.
I refer to your line about "old school method this is what we are doing as part of a EICR, what's the difference ?.Read through the link in one of above threads , code of practise for in service inspection and testing of electrical equipment
It would involve disconnecting in spur say and test with adapter to you pat test machine , that way it gets stored with all your other equipments information if you have an advanced pat tester
Or old school , ins res test and earth cont , visual , but keep records of tests , model test sheets are in the book
Basically a real ball ache , something we are avoiding , keeps you in work I suppose
It’s the way the records are kept or ours any way on hand written sheets and the two basic tests and visual carried outI refer to your line about "old school method this is what we are doing as part of a EICR, what's the difference ?.
HSE not houseMost company’s now a days will probably state you work to these codes of practises , ours does a long list in our electrical group rules
They do issue us with these documents (some where in the van )
If there is a fire or death through electric shock created by an appliance / equipment I’m sure the house will be looking for you maintanance / test sheets for this appliance / equipment
Including mechanical inspection sheets if required by whom ever