123

-
Arms
I've read various threads on faults and it's been suggested that an Earth Leakage Clamp Meter is an essential bit of kit and some suggesting it is the first go to bit of kit in fault finding.

What am I missing out on then? I do numerous call outs, and have yet to be beaten on one. What's it going to offer that some of my various bits of test equipment can't solve (IR Tester/MFT/PAT tester). Will it speed things up enough to pay for itself, or is it just going to be an expensive toy?

Thoughts welcome folks. My next purchase may be this, or a Dewalt DCE088D1G Green Laser (I already have a Dewalt DW087K Red Laser).
 
I actually use one of these, it's not officially sold as an earth leakage clamp meter but it performs well in the >5mA range. It means I don't need to carry two clamp meters unless the DB is over 400A plus the flexible clamp makes it very easy to clamp phase+neutral or 3 phases + neutral without too much manoevering of the conductors.
Chauvin Arnoux MA400D-170 Clamp Meter, Max Current 399.9A ac CAT IV 600 V | P01120575Z | RS Components - https://za.rs-online.com/web/p/clampmeters/7781040/

I have an earth leakage clamp as well for the odd occasion I need to accurately measure a value that's less than 5mA but I probably haven't used it in the last 6 months.

01.jpg

They do several models with higher current ranges and longer Rogowski clamps.
You'll probably find it cheaper in one of the UK based wholesalers.
 
It looks like for the time being I'll remain without an earth leakage clamp meter then. I can see in times ahead of RCD everything everywhere that it will have it's uses, but I'm failing to see how spending several hundred quid + annual calibration costs will even see one pay for itself, and it seems that it's not going to be an item that gets much if any use throughout the year.
 
It looks like for the time being I'll remain without an earth leakage clamp meter then. I can see in times ahead of RCD everything everywhere that it will have it's uses, but I'm failing to see how spending several hundred quid + annual calibration costs will even see one pay for itself, and it seems that it's not going to be an item that gets much if any use throughout the year.
Not sure it would need calibration.
Perhaps if you were using readings from it to fill in certificates.
 
agreed that is best but my little dilog one wont fit around 2x 25mm tails, I still saw a controlled and consistent increase in leakage clamped around the main earth
i have same problem with mine. clamp won't close round 25mm tails.
 
Millamp clamp meter or a good quality multimeter with low milliamp range connect on line with the earth/CPC works well. With the increase in RCD/RCBO protection being required for all circuits in the 18th edition. We will all have more nuisance tripping RCD faults to investigate
 
Excellent educational video.. thanks for sharing that.
I have to say I do own such a clamp meter but have yet to use it in anger.. it's at the bottom of my Spare toolbar somewhere... I Hope!
Circuit isolation, appliance isolation (usually cooker or immersion element) MFT and a bit of logic has always sufficed to date.. but also am aware of the increase in electronic gizmos can have an a cumulative effect.
 
Millamp clamp meter or a good quality multimeter with low milliamp range connect on line with the earth/CPC works well...

If I've understood you correctly, powering up an installation with a multimeter in series with a cpc or earthing conductor is a bad idea. If the multimeter internal fuse pops, you lose the earth and the exposed conductive parts are likely to rise to 230V.
 
I've had the lend of a Megger Earth Leakage Clamp Meter for a few days. Had a play around with it although typically no call outs...until today. Trying to wrap up for holiday a man down and they poured in. A good day to try it out, but my word, it's absolutely useless for everyday fault finding. It was my IR tester all the way. And damp and water ingress each time .

Its not something I think I'll ever need, it may have its uses as RCD everything gets ramped up and into commercial/industrial premises, but I have no use for it currently.
 
To be honest, you’d probably only use it for nuisance tripping RCDs. Check how much earth leakage there is on a circuit in normal use.
Another use would be to check whether the loading on a 3 phase installation was out of balance.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

123

Arms
-
Joined
Location
East Antrim, Northern Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Earth Leakage Clamp Meter...Why do I need one?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
58
Unsolved
--

Advert

Thread statistics

Created
123,
Last reply from
sunray,
Replies
58
Views
22,031

Advert

Back
Top