Hi, I am new to this forum and can't find an exact match to my search.
I am new to testing and inspection and have come across a db mounted in a garage on the wall whereby the t and e's for all circuits are clipped direct to the wall before entering the ceiling approx 1m above.
Is this deemed as a C2 or C3 on test cert?

Thanks.
 
I have to ask, what’s your electrical experience and qualifications?
 
Thanks all. My thinking is with reference to the condition report section 4.16 where the cables are not mechanically protected.

What do the regulations referenced in section 4.16 have to say about the example of wiring you are inspecting ?
 
The outer sheath is classed as mechanical protection. The environment the cables are installed in will dictate if it is sufficient mechanical protection. For example T&E clipped on a wall at high level with nothing around it would not warrant any code. T&E clipped just above a shelf used for heavy items may warrant a C2/3.
 
What do the regulations referenced in section 4.16 have to say about the example of wiring you are inspecting ?

Hi Andy. Thanks for your help on this. Really appreciated. I have re-read the sections in the regs and they refer to mechanical strain, not mechanical protection as I had read it earlier too hastily.
 
Last edited by a moderator:
The outer sheath is classed as mechanical protection. The environment the cables are installed in will dictate if it is sufficient mechanical protection. For example T&E clipped on a wall at high level with nothing around it would not warrant any code. T&E clipped just above a shelf used for heavy items may warrant a C2/3.

Thank you. I perceived the regs incorrectly.
 
A code maybe deemed necessary if the top of the consumer units IP rating (IP4X) is compromised where the cables enter the enclosure
 
might not warrant a code, unfortunately there isn't a code for an eyesore. it's R.A.F. ( Rough As F*CK)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Exposed T and E's during test.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
35

Thread Tags

Advert

Thread statistics

Created
MKSparky,
Last reply from
Timbo,
Replies
35
Views
11,222

Advert

Back
Top