Hi there, I'm looking for some advice regarding the above, I have a very basic type 'on/off sink/bath' switch on my copper cylinder immersion heater, I want to ad a very basic timer as mentioned above i.e. the mechanical dial types that have push/pull pins etc. the instructions that come with the timer I have attached..........my question is there are two 'live wires' (brown & Black) going to the elements in the immersion, from diagram 2 on the attached can both the 'live wires' be wired/connected into the same terminal in the timer....?

Wiring Diagram.jpg
 
If you have switch that says sink/bath you probably have a dual element immersion heater. Which element do you want timed?
 
If you have switch that says sink/bath you probably have a dual element immersion heater. Which element do you want timed?
yes I have one that says sink bath, do I just select which one I want to put on timer and wire it/connect it to the terminal, if so what do I do with the other wire......?
 
Your timer requires a permanent mains feed, so the only place that you can put it is in the mains feed to the bath/sink switch.
Then the timer will switch on and off the immersion you have selected with the bath/sink switch.

Is that what you want?
 
As above, it has to go before the bath/sink switch. As you are in Ireland you should consider getting a REC to do this.

Bear in mind that this cannot go in the hot press - if your installation is a number of years old then that is likely where the current immersion switch is. Also an immersion heater needs to be RCD protected.

If in any doubt consult a REC.
 

Reply to Fitting an 'APT Timer' to a dual Immersion Heater in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
133
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
813
Until last week I had a dual tariff electricity supply with a cheaper overnight tariff. This was good for the storage heating, but now the storage...
Replies
2
Views
2K
Hi, I'm about to switch to an energy tariff whereby i think it would be better/cheaper to heat my water via my immersion heater and not my gas...
Replies
10
Views
3K
Hey there! I am fitting four lights in my kitchen and have come across two issues (pictures attached - this is really the best quality I could do...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock