T
trick28
Hi All,
I am about to instal 100x30w fluorescent lights and was wondering if there are any rules that I have to apply in terms of switching these lights as I am concerned about having so many lights switched off one switch.
I also have been asked to install the lights using gear tray that allow 4 lights to be controlled of one tray. I have only ever used one ballast per light and was wondering if there are any hidden gremlins with these multiple trays.
what are they? T5
you can use multipole contactor/mcbs if you have to use one switch
normally a few switches,circuits- for maintenance ,avoidance of blackout etc.
the lamps are indeed t5s. I was planning to split the circuits into 3x6A c type breakers, an use 8 switches. Does this sound reasonable?
3 6A C type will be too tight anyhow
as far as i can tell a correction factor isn't needed for Hf ballasts
also Mk switches etc. don't require de-rating for fluorescent loads
there may be a bit of accumulated earth leakage with the HF ballasts ,not sure on harmonics-don't think it's a major issue
do you think that I should go for 3x10A c type breakers ?
I was also planning on breaking the switching up into 1 switch per 8 lamps using a 10 way switching panel.
I am using 1.5mm cable with the longest run being approx 20m
http://www.tlc-direct.co.uk/Book/6.2.1.htm
the method was a factor of 1.8 for demand and a factor of 2x again for switches
not as relevant now with the HF ballast and MK switches etc. except for number 3 -harmonics
i would be thinking 'minimum' 3 C10 or 5 C6 allowing for some losses etc. and not loading the circuits too much -the c6 may suit better for Zs and VD
fluorescent lights
Australia
trick28,
davelerave,