I have run 6mm t and e through the house from the db in the garage on a 32 amp mcb which is rcd protected. the 6 mm cable then goes into the back of an ip66 rated JB on the side of the house. i then intend to run 2 core (live and neutral) 6mm swa up to a workshop using the armour as earth.
my question is do i need to link the armour to the earth in the 6mm cable coming from the db in the garage and if so how do i do this.

On the other end, in the cu in the workshop i have got a 20 a mcb for sockets and 6 a for lights. how do i connect the earth block in the cu to the armour from the swa?
 
I would strongly recommend you get an electrician in to complete your works.

No disrespect, but your questions are basic ones however vitally important for the safety of your installation. Failure to have a broad spectrum of knowledge on the safety aspects of your electrical installation can lead to a simple but fatal error, unbeknown to you once installed.
 
my post concerned extraneous metalwork, if it's TNC-S system, the you need a 10mm bonding cable back to MET, ot TT the workshop.
 
Thanks Cid,
i will use a pirhana nut to connect the armour to the earth
thanks everyone for their input

Will you also be acting on the input to fully test and notify this circuit to building control ? Or are you just choosing to ignore the legal and safety aspects of this job in favour of the input that gets it done to your requirements ?
 
i appreciate your concern andy78,
of course it will be signed of and notified so rest assured all in good hands. my brother in law is a fully qualified electrician so he is more than capable of doing this
and i work under him ;)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bedfordshire

Thread Information

Title
How to connect SWA armour to 6mm Twin and Earth cable
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
A032701,
Last reply from
MJPD29,
Replies
16
Views
7,071

Advert

Back
Top