"Some Engineers" according to what the wall is used for, if its the inner skin of a cavity wall then is should be made good with a sand and cement this would be in the specification, in most case's the chase is left open for the spreads to fill with plaster, that is why "Some Engineers" are concerned, the inner leaf of a cavity wall can be 3.5N, 7N, or even up to 22N in a 3.5N block a chase filled with Bonding would be close the crushing strength of the block, but the Engineer can not rely on the site management or spreads to follow the specification, the days of the "Resident Engineer" have long gone and was the only way of ensuring the specification was followed, why Structural Engineers no longer have to spend six months on site before becoming qualified has baffled me for some time, this also applies to Architects, neither now days have any experience of what used to be called Buildabilty.
 
Regarding you point about rewiring it's always an advantage but in reality there is no way the bigger size T&E we now use can be pulled through. Oval conduit is already user unfriendly for rewires. I also don't think it is necessary to allow for future rewires (unless damaged).

I doubt the original intention was to provide for future rewiring, but it would be one added benefit in some cases. Obviously not every section of old conduit will serve that purpose, but think of 20mm round conduit dropping to a 1G switch plate - that's going to be easy to pull a cable through if the need arises.

I take it there's no chance of getting two legs of that new Irish T&E through 20mm?
 
I doubt the original intention was to provide for future rewiring, but it would be one added benefit in some cases. Obviously not every section of old conduit will serve that purpose, but think of 20mm round conduit dropping to a 1G switch plate - that's going to be easy to pull a cable through if the need arises.

I take it there's no chance of getting two legs of that new Irish T&E through 20mm?
If you pull 2 ends straight off the cable roller (no kinks), you will push them through a horizontal piece of 20mm pipe OK.
 
I doubt the original intention was to provide for future rewiring, but it would be one added benefit in some cases. Obviously not every section of old conduit will serve that purpose, but think of 20mm round conduit dropping to a 1G switch plate - that's going to be easy to pull a cable through if the need arises.
Your a lot younger than I thought, steel conduit drops where all about rewiring, using fabric covered cable needed this facility as the cable insulation deteriorated. :eek:
 
Your a lot younger than I thought, steel conduit drops where all about rewiring, using fabric covered cable needed this facility as the cable insulation deteriorated. :eek:
I’d disagree with you steel conduit is used to enable the use of single core cabling to provide a suitable means of protection and also enhance the space of wiring in single core cable you wudn be wiring a new build council office in twin and earth through galv it is single core so I don’t think age is a factor in your post
 
It is when you take into account when conduit drops where the normal thing to do, all switch's and sockets where cabled by a steel conduit vertical drop form the roof or floor void above or below, there where never any horizontal or zones, it was just straight drops to the sunken box, but as you say T&E did not exist it was always single core cable. It also made it simple, you just did not drill above or below a switch or socket.
 
It is when you take into account when conduit drops where the normal thing to do, all switch's and sockets where cabled by a steel conduit vertical drop form the roof or floor void above or below, there where never any horizontal or zones, it was just straight drops to the sunken box, but as you say T&E did not exist it was always single core cable.
All the drops I have done have gone into steel trunking and required a 90 degree bend sometimes included a set or double or even bubble at worst case lol I suppose different jobs have different specs but my experience with galv is that it’s galv all the way
 
never got the hang of that steel conduit stuff. put it on the bender. hit it with a sledgehammer to bend it... it squashed flat.
 
never got the hang of that steel conduit stuff. put it on the bender. hit it with a sledgehammer to bend it... it squashed flat.
A man of your experience should know better ?‍♂️
[automerge]1599252909[/automerge]
To be said in a broad Yorkshire accent: Eye when I where a lad, who'd of thought I'd be on ere talking about conduit drops in galvanised steel.
Who thought that times would change hey
 
Your a lot younger than I thought, steel conduit drops where all about rewiring, using fabric covered cable needed this facility as the cable insulation deteriorated. :eek:

I can only comment on that which I've encountered in domestic properties in NI and have very limited experience of this subject.

In my lifetime it was originally oval conduit and latterly round. These have all been one form of plastic or other.
 
I can only comment on that which I've encountered in domestic properties in NI and have very limited experience of this subject.

In my lifetime it was originally oval conduit and latterly round. These have all been one form of plastic or other.
You don’t tend to have steel conduit in domestic properties mate, oval pvc conduit or capping is more common, steel conduit is more commercial, industrial although I wudn be surprised if domestic rewires in 10 years time will have to be done in steel conduit with less money that is currently paid for a Rewire is disgraceful the lack of appreciation shown for sparks in most cases
 
You don’t tend to have steel conduit in domestic properties mate, oval pvc conduit or capping is more common, steel conduit is more commercial, industrial although I wudn be surprised if domestic rewires in 10 years time will have to be done in steel conduit with less money that is currently paid for a Rewire is disgraceful the lack of appreciation shown for sparks in most cases

The thread seems to be covering quite a range of situations, but I'd originally commented on posts that related to the slightly different practices employed in NI. Here capping is unheard of in domestic properies and PVC conduit is used anywhere that cables run in solid walls.
 
The thread seems to be covering quite a range of situations, but I'd originally commented on posts that related to the slightly different practices employed in NI. Here capping is unheard of in domestic properies and PVC conduit is used anywhere that cables run in solid walls.
What? Capping unheard of? PVC conduit run “IN” solid walls not “ON” is that what you do in Ireland?
 
Yes do it the easiest way you can, nailing a PVC capping over a T&E and calling it protected is the way the industry goes now days, it took a lot of skill and dedication to put in a steel conduit, even if it was just a straight drop or rise out of the floor, but as with everything, time is the biggest factor now days, speaking of which it's time I went to bed, goodnight all.
 
What? Capping unheard of? PVC conduit run “IN” solid walls not “ON” is that what you do in Ireland?

Conduit chased into walls, which the rest of the UK seems to think is crazy.

I can not state with absolute certainty that every spark works to the same standards, but accepted practice is to chase for conduit (pvc) and boxes before any cables are run.


To expand on this; on new builds the electrician will usually mark up walls and bring in another company to do the chasing as that's cheaper than doing so with their own time.
 
What? Capping unheard of? PVC conduit run “IN” solid walls not “ON” is that what you do in Ireland?
Yes do it the easiest way you can, nailing a PVC capping over a T&E and calling it protected is the way the industry goes now days, it took a lot of skill and dedication to put in a steel conduit, even if it was just a straight drop or rise out of the floor, but as with everything, time is the biggest factor now days, speaking of which it's time I went to bed, goodnight all.
steel conduit in domestic is not normal just capping is, goodnight ?
[automerge]1599255269[/automerge]
Conduit chased into walls, which the rest of the UK seems to think is crazy.

I can not state with absolute certainty that every spark works to the same standards, but accepted practice is to chase for conduit and boxes before any cables are run.
Depends what your talking about? There is a whole variety of specs some have surface conduit some have buried but yes all the containment is generally run in prior to installing cable that’s usually on the schedule of works and timescales but not in domestic works? Not talking about domestic rewires surely?
 
Last edited:
Depends what your talking about? There is a whole variety of specs some have surface conduit some have buried but yes all the containment is generally run in prior to installing cable that’s usually on the schedule of works and timescales but not in domestic works? Not talking about domestic rewires surely?

I've never known any electrician in NI to not use conduit when running buried cable down solid walls in a domestic property, whether it be a new installation or a rewire. It's standard practice over here.
 
I've never known any electrician in NI to not use conduit when running buried cable down solid walls in a domestic property, whether it be a new installation or a rewire. It's standard practice over here.
Wow! Conduit all the way over there then! Steel or pvc?
[automerge]1599255974[/automerge]
I've never known any electrician in NI to not use conduit when running buried cable down solid walls in a domestic property, whether it be a new installation or a rewire. It's standard practice over here.
Have the sparks heard of capping?
 
Wow! Conduit all the way over there then! Steel or pvc?
[automerge]1599255974[/automerge]

Have the sparks heard of capping?

PVC.

To be clear; I'm commenting only on domestic properties as I have no experience of commercial installations.

This house is three years old and round PVC conduit will be bushed into every box. There would be no issue with undercutting on price as every electrician will be expected to do this. As one previous poster had commented; an electrician would be laughed or thrown off site if they placed capping over cables, in place of conduit.
 
PVC.

To be clear; I'm commenting only on domestic properties as I have no experience of commercial installations.

This house is three years old and round PVC conduit will be bushed into every box. There would be no issue with undercutting on price as every electrician will be expected to do this. As one previous poster had commented; an electrician would be laughed or thrown off site if they placed capping over cables, in place of conduit.
Thrown off site? No you mean if the spark didn’t follow the spec for the job in question then he would be thrown off site. If it was a requirement to provide cabling in pvc conduit prior to commencement of works then of course that would be what the spark would do. So why would capping be laughed at? We are clearly on different wave lengths here. What about your occupied social rewires which I was doing in 1 day with a 3 man team? Do your sparks do that also?
 
Thrown off site? No you mean if the spark didn’t follow the spec for the job in question then he would be thrown off site. If it was a requirement to provide cabling in pvc conduit prior to commencement of works then of course that would be what the spark would do. So why would capping be laughed at? We are clearly on different wave lengths here. What about your occupied social rewires which I was doing in 1 day with a 3 man team? Do your sparks do that also?

I do not know whether or not any regulation mandates the use of conduit in such circumstances here, but it is standard practice.

Others will be better placed to comment as my experience is extremely limited, but I've never seen capping used over here or cables buried directly in plaster. This practice extends back at least over many decades.
 
I do not know whether or not any regulation mandates the use of conduit in such circumstances here, but it is standard practice.

Others will be better placed to comment as my experience is extremely limited, but I've never seen capping used over here or cables buried directly in plaster. This practice extends back at least over many decades.
Well you sound very experienced in my eyes and good that you voice your opinion, there are many regulations I can’t be arsed to go into all of them but to simplify it is to have rcd protection and all is well then. I’m sure most on here will agree that whilst carrying out a Rewire On domestic property will use capping Or oval conduit, unless it’s surface mounted and in that case it is trunking and with new regs fitted with fire clips.
 
Well you sound very experienced in my eyes and good that you voice your opinion, there are many regulations I can’t be arsed to go into all of them but to simplify it is to have rcd protection and all is well then. I’m sure most on here will agree that whilst carrying out a Rewire On domestic property will use capping Or oval conduit, unless it’s surface mounted and in that case it is trunking and with new regs fitted with fire clips.

I wouldn't argue against practices commonly employed in other parts of the UK, although the use of conduit here does have certain advantages - primarily the ease with which a cable could often be replaced if necessary.
 

Reply to In your country, do you use pipe to run wire through very much? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock