Hi I live in the Highlands of Scotland and I am doing a EICR. The main supply is a 2 core cable supplying phase and neutral and a seperate bare earth wire. I cannot tell if this earth wire goes to an earth rod or to the distributors earth system. How can I check this. Thanks
 
PEFC and PSCC, if they're the same (give or take) then it's TN-C-S. If Ze is above TN-C-S limit but below TN-S then it's possibly TN-S. If it's way over then think TT.
Given that it's out in the sticks I'd be expecting TT

- - - Updated - - -

Just re read the question, does the bare earth go to a clamp on the incoming cable?
 
Hi I live in the Highlands of Scotland and I am doing a EICR. The main supply is a 2 core cable supplying phase and neutral and a seperate bare earth wire. I cannot tell if this earth wire goes to an earth rod or to the distributors earth system. How can I check this. Thanks



Well, ....if the earth conductor doesn't originate at the service head or from the incoming DNO cable sheath then it must be coming from an earth rod or other form of earth electrode!!
 
check pipework isn`t being used as the means of earthing...
is there a private borehole here?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Incoming Earthing
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Steve1968,
Last reply from
GLENNSPARK,
Replies
3
Views
1,483

Advert