Hello everyone..
I have a job tomorrow tracking down a tripping RCD fault.
This would have panicked me a year ago, now I'm looking forward to it and cant wait to get there!
However, from the phone conversation I have discovered the following:
1. No recent DIY work or professional work has been carried out recently.
2. One of the RCD's (dual board) trips every 5-40 minutes, this RCD feeds the kitchen ring, all lights and one other circuit (forgotten which)
3. It does not trip at any regular time of the day (so possibly fridge or other irregulary timed power source)
4. It started approx 3 days ago, nothing 'different' happened at that time. No new fridge, cooker etc.
5. Sometimes trips when different appliances are switched on, sometimes just spontaneously.
Basically the prelimanary detective work has given me little insight into the problem so I will be relying on IR testing and earth leakage clamp meter. I expect/hope that the global IR test will show a poor reading so then it will be a simple job of narrowing the fault down. However..
I do like to try and have a plan for any eventuality, so this is my question:
1. If the IR tests show no fault then where do you go from there?
I know I'm being a bit ----, but I like to play it a bit like a game of chess and think many moves ahead!
My thoughts are (given good IR results):
- homeowner could leave one of the affected circuits switched off and see if RCD stops tripping.
- Check all items that get plugged in for earth leakage.
- Visual inspection of O/S lights for poor IR.
- continuity tests between neutrals of differing RCD's (highly unlikely given fault has only just started occuring)
- RCD tests, including ramp.
- Check for loose connection upstream of RCD.
Have I missed anything that you guys would automatically do/think?
I think with the recent posts about this topic , the most valuable test once the preliminary tests of the circuit have been done is the ramp test with appliances connected and without , that would indicate what appliances are faulty , you can keep trying it and unplugging appliances until the readings improve to narrow it down ..
Reactions: 3 people
as above. ^^^^.
Had this the other day, eventually traced to a twisted bit of cable on the kitchen ring main - took hours to find - had been happy for years, but after time it started to trip occasionally, then more frequently and then a couple of times an hour, thats when we were called.
Reactions: 2 people
Thanks Ray,
I'm unsure how having the appliances connected, unconnected affects the Ramp test though? Doesn't the ramp test just show at what mA the RCD is tripping when you put the fault current through it?
One that got me on an intermittent was not leaving the earth cables connected in the bar testing between cores on IR. The cable cores were clear to each other, but the live was down intermittently to the general mass of earth which I had eliminated by taking the earth cable out of the bar. Gggrrrr.
When the installing electrician stripped the cable back for the outside light, he had ringed the insulation on the live that was touching the brickwork as it came through the wall. Sometimes it would trip every couple of weeks. Sometimes every couple of days. Very frustrating trying to fault find a fault that isn't there when you attend, but get a phone call a week later to say it's tripped again!
You can have this little gem for free, as long as you let us know what it was when you find it dude.
x
Reactions: 5 people
if you ramp test with no circuits connected and get, say, 25mA, then with circuits/appliances connected get 10mA, that says there's 15mA leakage.
Reactions: 4 people
On pretesting,one that got me was some outdoor spike lights that are class 2 with twin flex in use , and someone had clipped twin flex around to adaptable boxes ,with the lighting circuit with CPC disconnected at the DB it was all clear , But testing down to the MET it was down , eventually found a buried adaptable box wrapped up in a carrier bag ,
Reactions: 3 people
Thanks Ray,
Thats the most valuable part really because your testing with the leakage there , as Tel says the readings will tell you which appliance is registering the most when they are isolated ( i.e. the difference ) as you unplug items
Stick an earth leakage clamp meter around the tails, turn off each MCB in turn, noting the reduction in the overall leakage.
This may show something useful and save you hours!
Reactions: 5 people
Hello everyone..
Give it a full test properly as per GN3 this way you wont miss anything out, and wont get confused its easy to jump the gun when fault finding and ending up going round in circles. Make sure that there is nowt connected and all fused spurs are switched off.
Con, IR, Zs (at every socket) and then RCD and ramp. If that goes well, then i suggest checking for the obvious and easy first. Loose connections and check the socket to make sure that the plug is snug fit and doesn't move about due to wear, or pull out too easily.
Good luck and let us know how it goes.
Cheers.............Howard
Reactions: 1 person
Thanks for that Howard, very sensible advice.
Quite frankly I dont think that fault stands a chance now!! I'll give it one hour... tops!! :smile5:
Reactions: 2 people
Can't wait for the updates on this one!
I'd be asking about leaks, DIY, outdoor connections, ...........
Well you know you'll be getting an update Murdoch, perhaps not over the next few days but it'll come. Plus it'll be an honest one, even if it means I missed something silly, so you may be in for a good laugh!
Intermittent RCD trips are the worse, especially on upfront or dual RCD boards!
The last one I had was due to accumulated earth leakage across one of the RCD's so virtually any extra load on the circuit may push it over.
Fortunately I had installed a hi integrity board (which is the norm for me these days) so moved the "worst" circuit onto its own RCBO!
don't rely on IR test. i had one last week where a L cable in a socket had a nick in it, pressing against the back box. MCB and RCD both tripped after energising circuit for about 1 minute. IR test on the circuit showed 15Megohms.
Reactions: 4 people
Sensible! Do you find you lose some quotes Murdoch with the higher cost of the 'hi integrity' board and RCBO's?
BG hi integrity board £50.
Reactions: 2 people
The install is designed to fit in the MCB's ways within the hi int board, leaving 2 ways spare by the main switch. All my board change estimates include
"NB: If problems are detected during the fuseboard change additional work may be required. Such issues and associated costs will be discussed with you, prior to being implemented"
So the customer cops the additional cost of the RCBO and remedial works.......
The most recent one was where the house had a borrowed neutral on the lights, with absolutely no way to run a cable or fix it... so combine up and down circuit onto 1 x rcbo and everybody is happy.
My pricing locally is lower than most from what I hear, but I'm happy with what I make doing a CU change as its a good rate for 1 days work. Sure there are a couple of "chuck it in anyway" cowboys, but most of my customers won't let them work in their houses once they have met them!
Reactions: 1 person
...Good advice,and don't start the CSI craic,until ALL standard tests have proved non-productive. I had an intermittent RCD trip,on a split way recently,no rhyme or reason,not for weeks,then won't reset,then fine...Narrowed to lighting circuit,which was both floors,a mix of old VIR in conduit,and new.It went from not resetting on a N-E fault,to a clear IR result,whilst i was jogging up and down the place. In the end,i left the MFT at the DB, IR locked,with threshold alarm set highish,and marched about some more...a tread centre of landing,upstairs,gets a beep!...carpet up,loose boards out,and there are two VIRs bent round the end of a section of displaced old conduit,which has come 20mm out from a Tee,the board slightly pressing on said item...Felt like i'd found the Golden Chalice...customer said "Oh".........so all worth it :icon12:
Reactions: 8 people
This may sound strange HHD but with no fault finding preconceptions you may have the benefit of not proceeding down 'well worn experience based' routes. More times than not this method will find a fault quickly. But frustratingly if the fault is not found quickly it can be a while to reconfigure yourself to start from scratch methodically which can waste time. I am speaking from an experience of fault finding on equipment systems here rather than fixed wiring installations but same principles in fault finding.
Which MFT were you using PEG?
Id put it down to a thermal related neutral to earth fault where a screw has nipped the neutral so when that point it warms very slightly causing the RCD to trip ,could be anything great fun these faults to find
3 years on the forum and still asking about RCD faults?
There’s only one way to find a fault, go and test the damn thing!
People on here will guess or come up with “I had xxxx last week”, non of which will help.
Reactions: 2 people
.............How old is the fridge and freezer if they are on the tripping RCD
I hate faults where its not clean cut as to what it is, i usually start by scratching my head thinking hmmm... I wonder where to start.
Its not too bad when its a nice modern house, but its when its an old cottage or something like that where it becomes a nightmare.
Ah, the true GG! I can kinda see where you're coming from Tony. On the other hand, I find it good for guys to tell us about faults they have found and how....it all adds to my/our knowledge.
Now, If only PEG would tell us about the mft that lets him do the trick he described.....
Which MFT is that?
Could be all those nice Christmasy items plugged in all over the place, internal as well as external. Have fun.
Got there at 8am, found the fault by 9am, home with a cup of tea for 9.30am :smile5:
Actually I was a bit disappointed, I was prepared for battle and It wasn't even a minor skirmish!
Global IR test on faulty side showed 0.000MΩ, Only 3 circuits, so quickly broken down to discover fault was on the kitchen ring.
The house was pretty much a building site and was a complete DIY wiring job which the chap was quite happy to admit. He had a plug in one of the sockets which went into a cupboard and then fed another double socket on the side of the cupboard. This was the faulty set up and as soon as I unplugged it the fault cleared! Still feels good though finding it...
Good Morning to you as well Tony, hope you have a happy day you cheery fellow :smile5:
Reactions: 8 people
Post removed as I felt guilty!
hope you charged him well. bloody DIY plonker.
Reactions: 2 people
Removed as I felt guilty!
Drat! I should have done a 'reply with quote' while I had the chance.
I was going to ask whether you'd had a glass too many with your lunch.
Reactions: 1 person
Ha Ha, I wondered if anyone saw it! I was tempted to leave it but thought better of it!
you're allowed to say "arse". it's in the oxford english dictionary.
The first thing I do with a fault is forget everything the customer tells you!!!lol
No DIY work my Ar3e!!
Jay
It was actually his wife that had said 'no recent work'. He was happy to explain everything he had done recently... which included the extractor fan, 2 spurs and the 'faulty plug/socket'. The only good point was that he could tell me the exact layout of the ring in the kitchen!!
HappyHippyDad
Supporter
Gloucestershire
United Kingdom
Intemittent tripping RCD.
HappyHippyDad,
Guest112,