Lucien Nunes
could of being a neutral to earth fault causing the trip
No, this could not have been the problem as it was an MCB tripping, not an RCD.
could of being a neutral to earth fault causing the trip
As Lucien says^^^^ As the electrician you should already have a clear understanding of protection device's functionalities and what type of fault you are expecting to be looking for. Hence the suggestions previously mentioned regarding checking the current flowing through the device.great find on the boiler earth could of being a neutral to earth fault causing the trip when the boiler fired up
I forgot to clarify, for an mcb you would be looking for the total load current to see if or when it is exceeding the rating of the device. For an RCD you would be looking for the total current imbalance to see if or when that is exceeding the rating of the device. For a combined rcd and mcb (rcbo/rccb) you would be looking at both.As Lucien says^^^^ As the electrician you should already have a clear understanding of protection device's functionalities and what type of fault you are expecting to be looking for. Hence the suggestions previously mentioned regarding checking the current flowing through the device.