Gents,

Looking at an install which will include two new circuits, one for lights and another for a ring main. There is no space on existing 16th edition board and customer does not want a new 17th edition board, there is no double pole isolator before it.I am planning on Henley blocking the supply and taking a live and neutral to a new RCD 2 way unit. What's puzzling me is... As there is a requirement to have a main switch for isolation rather than using an RCD main switch as the isolator, would I install a double pole isolator external to the rcd unit to meet regs? Already explored ideas of RCBOs with a standard main switch 2 way unit but clients costs are the issue. Thanks
 
If your being forced to cut corners to keep costs down then it's time to walk away imho. I must admit not being allowed to use a RCD main switch as a main switch is new news to me. I guess you never stop learning :)
 
Why do you want a main switch for isolation instead of using the RCD in the board

There is possibly more argument for a single isolator for both installations, albeit not necessarilly required
 
RCDas main switch in your new board is fine, but fit a 100A D/P isolator before the henleys ( installation should have a single point of isolation ).
 
I must admit I even thought two main switches was acceptable if very clearly marked that there was more than one main switch. Obviously avoid this at all costs in the first place.
you`v got to look at it as an installation intended to be used by unskilled/uninstructed person/s not under supervision n all that lot....
so a single point of isolation makes common sense...doesn`t it...
 
Oh yeah, totally agree. Only place I have ever seen it was in a Secondary school on a condition report done by someone else.

We accepted clearly laballing at each main switch that another main switch needed to be switched off for total isolation in a nice tref label. I would never install anything this way to boot. I definitely wouldn't do it in a domestic property.
 
you`v got to look at it as an installation intended to be used by unskilled/uninstructed person/s not under supervision n all that lot....
so a single point of isolation makes common sense...doesn`t it...


what a waste of words when a simple "muppet" would do
 
Another way to do it if you don't have any spares / only one spare in the existing board is take a supply from an MCB in the existing board to feed your new board and if necessary move a circuit from the existing board into your new board. Not always possible or practical depending on the condition of the old board and circuits.
Advantage of doing this is it all remains on the existing mainswitch and you don't have to pee about with putting henley blocks into the tails which you obviously can't isolate because nobody can break the seals (nudge nudge wink wink etc etc)
 

Reply to main isolator switch in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock