- Reaction score
- 516
Anybody else picked up on this yet?
Here's from another forum:
(thanks ecogen)
Here's from another forum:
(thanks ecogen)
G83/2 is due to be issued around mid March. Consultation closes Friday 3rd March
http://www.energynetworks.info/stor...tions/ER G83 - public_consultation_211211.zip
Installers and other interested parties may wish to look at the wording in,
Master_ER_G83v5_9_Dec_2011_dcrpPC_draft
2. SCOPE.
5.1 Connection Procedure. 5.1.1 Single Connection Procedure.
5.8 Voltage Unbalance.
Appendix 1 connection procedure flow chart.
and
ER G83 - public_consultation_211211
2.8 Voltage Unbalance.
My concern is the meaning of single customers installation and single installations.
Customers installation is defined in 4. Definitions. The electrical installation on the Customer's side of the Exit Point together with any equipment permanently connected or intended to be permanently connected thereto.
Does the word single now make these the only SSEG on a transformer or feeder?
G831/1 Annex A allows for the DNO to propose changes / reinforcements in the event that a SSEG causes operational difficulties. This was seen in part to conflict with install and notify. Annex A has been significantly revised in G83/2 with this and other sections removed or integrated elsewhere in the document.
If single does mean the only SSEG on a feeder or transformer then the installer would in effect have to contact the DNO in advance to find out if a SSEG is in commission.
4. Definitions. Close Geographic Region. 3) Has a PV installation been commissioned within 500 metres of the proposal.