Anybody else picked up on this yet?

Here's from another forum:

(thanks ecogen)

G83/2 is due to be issued around mid March. Consultation closes Friday 3rd March

http://www.energynetworks.info/stor...tions/ER G83 - public_consultation_211211.zip

Installers and other interested parties may wish to look at the wording in,
Master_ER_G83v5_9_Dec_2011_dcrpPC_draft
2. SCOPE.
5.1 Connection Procedure. 5.1.1 Single Connection Procedure.
5.8 Voltage Unbalance.
Appendix 1 connection procedure flow chart.
and
ER G83 - public_consultation_211211
2.8 Voltage Unbalance.

My concern is the meaning of single customers installation and single installations.
Customers installation is defined in 4. Definitions. The electrical installation on the Customer's side of the Exit Point together with any equipment permanently connected or intended to be permanently connected thereto.

Does the word single now make these the only SSEG on a transformer or feeder?
G831/1 Annex A allows for the DNO to propose changes / reinforcements in the event that a SSEG causes operational difficulties. This was seen in part to conflict with install and notify. Annex A has been significantly revised in G83/2 with this and other sections removed or integrated elsewhere in the document.
If single does mean the only SSEG on a feeder or transformer then the installer would in effect have to contact the DNO in advance to find out if a SSEG is in commission.
4. Definitions. Close Geographic Region. 3) Has a PV installation been commissioned within 500 metres of the proposal.
 
See also this from Martin Cotterell of Sundog

The draft includes a number of significant changes from G83/1-1, including:
Inverter requirements
• Two-stage protection settings – aligned with G59/2 (based on 230Vac nom)
• New short circuit current contribution test
• New frequency drift and step change stability test
• 180s start up delay shortened to “20 – 60 seconds”
• DC injection limit adjusted (20mA limit for generators up to 2kW; Larger systems – 0.25% of the AC current rating of the device) • Power quality tests (including DC injection) to be done with a minimum system of 2kW. Where an inverter is less than 2kW – inverters to be tested in a group • Adoption of BS EN 62116 anti-islanding test procedure
Connection requirements
• Clarification and renaming of 2 stage application process … to make it clearer and easier
• Clarification on definition of “close geographical region”
• Significantly simplified application forms
• Requirement for AC isolator next to consumer unit to change to isolator located “in an accessible location”

Martin's original post here:
ER G83/2 draft for public consultation - The solar PV blog » The solar PV blog
 

Reply to New ER G83/2 2012 in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

C
Hi Guys, We installed a 3.68kw Solar PV on a property in October 2012, sent off the DNO application G83 Commissioning form and all went through...
Replies
1
Views
936
A new draft version of the G83/2 regulations has been released for consultation including major changes to the rules about when advance permission...
Replies
42
Views
10K
Interesting discussion today with WPD, (My favourite DN0 :) ) with regards to extending an existing 3.68kW system. One pole, two overhead wires...
Replies
7
Views
2K
Ian-LS
I
We've received a note from WPD with an application which has been approved in South Wales which is out of our usual area although same DNO...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock