Hi I have put new socket in hall and ran cable straight to consumer unit,and connected to downstairs sockets . But it keeps tripping . I have used about 10 metres of cable .
Why would this be any help be grateful.
So you have spurred directly from the MCB ?is the CU a modern type ie does it have 2 RCDs?
Have you connected the N to the correct N bar?
 
I disconnected again but totally puzzled checked cable and changed sockets but still no joy .

33BF0361-7D53-4D3D-83B6-EBC15BE04E4B.jpeg
 
I disconnected again but totally puzzled checked cable and changed sockets but still no joy .

View attachment 42516
Of the 2 N bars, which one are the existing RFC Ns connected too, whidhbar did you connect thre new N into, can you see what people are getting at? Have you IR tested your new addition?
 
Last edited:
Some observations:

1. The OP has been reviewing the thread recently and hasn't done the decent thing and updated us or responded to any of the points raised

2. This is clearly a business installation for a client....

3. A new circuit is subject to Part P of the building regs if in a domestic property

4. ANY electrical changes in clients properties should be designed, installed and tested to BS 7671 AMD 3, by a competent person with the appropriate test equipment....

5. Lets hope his PL insurance covers such work................
 
Also noticed from the picture op is going to 32A mcb but stated he ran a cable to the board from the socket. No mention of a ring so im assuming its a spur.
Assuming say Clipped Direct max amps for 2.5 T&E in the BYB would be 27A not taking in to account thermal insulation & ambient temp etc. adjustments if required.
 
Some people try to argue that spurring from the mcb is not a new circuit as it uses one mcb & would not be notifyable
like say putting smoke detect circuit on with lighting?

others argue any new cable installed in to the CU is notifyable
It's not a new circuit, you can spur from any point on a RFCthe MCB included.
 

Reply to New sockets fault keeps tripping in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top