Discuss New sockets fault keeps tripping in the UK Electrical Forum area at ElectriciansForums.net
Hi I have put new socket in hall and ran cable straight to consumer unit,and connected to downstairs sockets . But it keeps tripping . I have used about 10 metres of cable .
Why would this be any help be grateful.
So you have spurred directly from the MCB ?is the CU a modern type ie does it have 2 RCDs?
Have you connected the N to the correct N bar?
I disconnected again but totally puzzled checked cable and changed sockets but still no joy .
Of the 2 N bars, which one are the existing RFC Ns connected too, whidhbar did you connect thre new N into, can you see what people are getting at? Have you IR tested your new addition?
Is it just me, or is there less neutral cables than there is live?
Problem could be at the socket. Live cable squashed against fixing lug for example.
Reply to New sockets fault keeps tripping in the UK Electrical Forum area at ElectriciansForums.net
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...