irishsailor

My mate has an outside light problem, he lives in a masonette, his light has stopped working, he called out building services the guy said it weas wired in a way that the internal conduit was used as a line conductor?? does this make sense or has anyone come accross this problem before?? If so can anyone suggest a solution??

Regards

Chris
 
My mate has an outside light problem, he lives in a masonette, his light has stopped working, he called out building services the guy said it weas wired in a way that the internal conduit was used as a line conductor?? does this make sense or has anyone come accross this problem before?? If so can anyone suggest a solution??

Regards

Chris
Never heard of conduit being used as a line conductor.Wouldn't it mean all the conduit in house would be live then:confused:
 
Guys

I have had a look at the light, it is in an old metal conduit, 2 cables exposed. I have tested between conductors, I believe the conduit is acting as the cpc. However the voltage jumps between 125ish to 240

Any suggestions

Chris
 
Guys

I have had a look at the light, it is in an old metal conduit, 2 cables exposed. I have tested between conductors, I believe the conduit is acting as the cpc. However the voltage jumps between 125ish to 240

Any suggestions

Chris
If building services came out earlier,is the property council or rented.Maybe the property needs rewired,is there any earths in the property:eek:
 
sounds to me like you have dodgy continuity on the conduit. this is presuming that the light works all the time i.e. it doesnt flash.

It would be helpful to know what you are testing against i.e. are you testing from the conduit to the live or the neutral? it would be interesting to test against a known good earth and note the reading.

Metal conduits induce voltage if they are not earthed properly and this can give odd readings.

Solution:

Run an earth wire from a known earth through the conduit to the light fitting. try and earth the conduit to this earth cable at either end. this should solve it. failing this you will need to rerun the conduit and make sure its connected to the other conduits in the system substantially.
 
Cheers Marky

The conduit is in the frabic of the structure so it would be difficult to reinstall arrgghh , yes testing from the conduit against Line & Neut. Will look at running a know good earth. It is a good learning curve for me, bloody pulling my hair out well whats left if it.

Chris
 

Reply to Outside Light Problem in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock