A

abdulrahman42

Hi All,

I am a little bit confused, I have just bought a house and the boiler and whirlpool bath are connected together to a 16amp breaker, I know the boiler should have its own supply but this is what I got.

Anyway if the boiler or whirpool is turned on, it trips the RCD. Ive disconnected the boiler and turned the whirpool on and vice versa but still the RCD trips. Ive checked the resistance on the appliances and both are good but they are old and my metre might not be great.

Ive put the supply to a 32 amp breaker just to see if the RCD trips however it doesn't and both work. Im confused about the fact that if there was an earth leakage fault I assumed it would still trip the RCD even on a 32 Amp breaker.

Am I missing anything as I'm not sure what to do next. Please Help.

Regards.
 
There is nothing to say that the boiler must have its own supply.

Can you post some pictures of the consumer unit where the RCDs and mcbs are so that we can see what you have?
Moving the circuit from a 16A circuit breaker and onto an RCD only could be extremely dangerous as a circuit breaker and an RCD provide different types of protection.
 
I have not put it onto an RCD i Have put it onto a 32 amp circuit breaker.

i have put it back to the way it As I'm not 100% sure it's safe to put a boiler or whirlpool bath on a 32 amp breaker.
 
I have not put it onto an RCD i Have put it onto a 32 amp circuit breaker.

i have put it back to the way it As I'm not 100% sure it's safe to put a boiler or whirlpool bath on a 32 amp breaker.


Is the 32A mcb that you changed it over to protected by an RCD?
 
I have not put it onto an RCD i Have put it onto a 32 amp circuit breaker.

i have put it back to the way it As I'm not 100% sure it's safe to put a boiler or whirlpool bath on a 32 amp breaker.

It all depends on the design of the circuit and the particulars of the installation as to whether it is safe or not.
It is certainly not safe to move a circuit with a known fault on to a larger sized protective device just to see what happens.
 
  • Like
Reactions: 1 person
I agree with Murdoch, time to get someone in. The fact that you changed the MCB to see what happens i.e. will the RCD trip, says to me that your knowledge is a touch limited. Not having a go, but we all have our limitations.

RCDs do indeed detect earth faults, correct. Out of curiosity it was the RCD and not the 16A MCB that was tripping?
 
  • Like
Reactions: 2 people
As far as I'm aware it is, But I will double check, If it's not then I assume there is an earth leakage fault is that correct.

As Murdoch said you cannot assume anything. If the rcd only trips when the circuits are connected to the 16A mcb and not the 32A mcb then why would you assume its an earth leakage fault?

No offense but from what you have posted so far it appears that you have little knowledge in how mcb's and rcd's work and what their functions are in an electrical installation. You could be putting yourself and family at risk if you attempt to correct the problem in the manner to which you tried.

Get a qualified spark in to test it properly and to check that the circuits have been installed correctly. (that's my professional advice)
 
Last edited by a moderator:
  • Like
Reactions: 2 people
Op I think it is time to get someone more experienced in and let them sort it for you, Fault finding on a circuit by presuming and guessing isn't the way to go about it.
Maybe offer up your location and one of our members may be able to come and sort it.
 
  • Like
Reactions: 1 person
he'sin brumingam
 
  • Like
Reactions: 1 person
Can I just chuck my thoughts in here, it says in your profile that you are a trainee electrician. Obviously, from your posts, you are very unsure of what you are about, so why don't you talk to whoever your trainer/mentor is? can we assume from your nick that you are 42? If so, how are you training?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCD tripping
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
abdulrahman42,
Last reply from
sparksburnout,
Replies
16
Views
2,571

Advert