skts x 2 earth terminals

Discuss skts x 2 earth terminals in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
229
Been 2nd fixing today, which i've not done for many years. I've noticed that both Volex 13A twin & single sockets have 2 x earth terminals. Is that now standard? I thought that requirement was only applied to sockets that served a lot of IT equipment. Even years ago i would sleeve the earths separately, but then into one terminal. Is there any electrical reason for the change? Thanks
 
There are arguments for both.
Twisting together would allow for continuity of the conductors, if the terminal became loose.
Twisting together restricts the number of conductors that can be terminated.
Twisting together is a pain when it comes to testing.
 
I cannot see the problem myself, if you connect the CPCs into seperate terminals and one breaks or isn't tight the socket is still protected, if in one terminal then the same as it always has been, who cares, it is no big deal either way on a standard domestic outlet.
 
Some sockets have 2 terminals for each of the circuit conductors.
This increases installation times and increases the likelihood of a termination loosening.
If one terminal fails, then yes the conductor is still connected, though using a plug in tester would not show that a conductor had fallen out.
 
I cannot see the problem myself, if you connect the CPCs into seperate terminals and one breaks or isn't tight the socket is still protected, if in one terminal then the same as it always has been, who cares, it is no big deal either way on a standard domestic outlet.
i can't see it making any difference what so ever. However, as not in the game as such I just wondered why the introduction. Surly must be more expensive to produce, therefore there must be a reason why. Could it be an EU instruction?
 
Presumably it is to enable the socket outlet to be used where there are high protective conductors currents.

Personally I would always use both terminations.
 
i can't see it making any difference what so ever. However, as not in the game as such I just wondered why the introduction. Surly must be more expensive to produce, therefore there must be a reason why. Could it be an EU instruction?

EU are not interested in UK sockets....the reason is manufacturers dont have to manufacture both types....cheaper to tool for one only,and the extra cost of the two terminals is sneaked onto us.
 
In fault-finding an RFC with a higher-than-expected value for r2, on at least a couple of occasions it has turned out to be due to relying on the socket internal metalwork.

One end of the RFC into one terminal, the other end of the RFC into the other terminal. Screws done up tight. But the sockets had riveted bits of metal work, not always making good contact. I've seen sockets with the best part of an Ohm measured between the two terminals.
 
I had the exact same issue about 6 months ago. It was a single socket that had been connected up that way causing the issue. I re terminated them and the lowered the value however after reading this thread i was thinking the terminations just may have been a bit crap!
 
Decent sockets with double pole switching, will have 2 earthing terminals. The cheaper single pole switched sockets - which I stay away from, normally have just the one earth terminal.

I personally will use both earth terminals on a newly wired sockets only because it looks better. On a refurb/replacement socket, I'll use whichever terminal is best for the existing cable length.

Earthing of the metal knockout boxes in domestic applications, is of course not required providing one of the mounting lugs is fixed.
 
Well i would personally use one of the socket earth terminals for the rings circuit conductors, and the other for a flying lead to the back box. I don't really care what BS7671 has to say about relying on a face plate fixing screw, i was taught to use flying leads to the back box and see no reason not to continue to do so!!
 
Nothing wrong with flying earth leads inside the boxes - I was taught that way back too. However, back in the old days of the 60's & 70's, you really did need flyleads. Limited use of rcd's and no knockout box grommets was common place - how many original socket boxes from this era do you find without any grommets?
 
There does appear to be a misinterpretation of the requirements for 2 separate CPCs for such circuits.
One conductor run in a ring formation and terminated at separate terminals does not equate to two CPCs.
It needs two separate conductors, each connected to a separate terminal in order to comply.

Im not sure what your saying Spin?
Are you saying the image (for example) in Guidance note 8 page 132 is incorrect!
As it says on page 131 that if the ends of the protective conductor are separately terminated at DB & sockets then Reg 543.7 will be met as shown in image
 
Hey guys. Haven't been on in a while but is this really what it's come to arguing over how many earth terminals to use in a domestic socket. Does it actually matter. ...........

Sent from my GT-I9505 using Tapatalk 4
 

Reply to skts x 2 earth terminals in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top