Went to look at wiring a biomass boiler today ...
boiler and buffer tank located in a breeze block out building sat on concrete pad .
PME earthing system , existing supply to outbuilding in 25mm 3core swa .
ALL the pipework was in place (copper and steel pipe) connecting buffer tank and boiler .
Mains water also in place in nice blue plastic pipe .
Grabbed the wander lead and tester out of the van to test if the metal pipework was extraneous
and low and behold got a dead short . also dead short from unistrut on walls to earth (which is bizarre as
it is not in contact with anything metal) . :rolleyes4:
So does concrete conduct electricity ? this is the only plausible answer .
i meggared between the concrete pad and earth at 500v with 32Mo resistance , so not conducting well !.
the buffer tank is 3000 litre and has a large metal footprint sat on the concrete pad .
im going to bond the pipework but am gobsmacked as to how it has become an extraneous part .
your thoughts on this please .
boiler and buffer tank located in a breeze block out building sat on concrete pad .
PME earthing system , existing supply to outbuilding in 25mm 3core swa .
ALL the pipework was in place (copper and steel pipe) connecting buffer tank and boiler .
Mains water also in place in nice blue plastic pipe .
Grabbed the wander lead and tester out of the van to test if the metal pipework was extraneous
and low and behold got a dead short . also dead short from unistrut on walls to earth (which is bizarre as
it is not in contact with anything metal) . :rolleyes4:
So does concrete conduct electricity ? this is the only plausible answer .
i meggared between the concrete pad and earth at 500v with 32Mo resistance , so not conducting well !.
the buffer tank is 3000 litre and has a large metal footprint sat on the concrete pad .
im going to bond the pipework but am gobsmacked as to how it has become an extraneous part .
your thoughts on this please .