It's a pitty SWA cables are so crap now. Under M&Q and foundry regs no CPC is required. The cables had 1 tinned copper to 3 steel wires in the armouring. Better still install PILCDWA the return path was often better the conductors

Thank god I've retired :D
 
Last edited by a moderator:
OK. GN1 specifies that for 35mm SWA the armour is an acceptable CPC. But here comes the runt.
Irrespective of the Regs, (or is it in very strict adherence of the regs?) the MET must be at the supply head and the main bonding must run to the MET. It is unacceptable, and they will NOT provide a connection, if the bonding is to a Dis Board fed from a sub main.

Also, tails of more than 3 meters are Unacceptable. If the tails would be more than 3 meters then you have to install a single way DB (switch fuse or other) within 3 meters and take the sub main from that. More over, and contarary to the EDF web site which only requires an isolator, but only in some areas, it must contain fuses (or I suppose some other form of cutout) . The Reason... "so that they do not have to change their fuses if there is a fault with the sub main". ... Sounds rediculous to me because there is no discrimination, however that is their requirement before thay will connect a meter.
 
Last edited:
I was under the impression that the tables in GN1, that refer to sizes of armourings in SWA, were an indication to whether the armourings comply with table 54.1 (54G in 16th). If the armourings do not comply then the adiabatic equation needs to be done in order to ascertain whether the armouring are capable of taking the current produced under earth fault conditions.
 

Reply to SWA for 3 Phase Installation in the Electricians' Talk | All Countries area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock