Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a 16mm 3 core swa and is fused at 63amps with rcbo feeding sockets lights etc.
I have now built a cabin further down the garden and want to provide another CU in it for sockets and lights. It will be an outside office. I can’t run a feed back to the house so my question is can I take an additional feed of off the garden CU into the cabin and have another CU there. If so what would be the Fuse Isolator rating for the new CU in the cabin. I do have enough 10mm 3 core swa to run to the cabin. Assume no heavy loads on Garden or Cabin as it’s all low power stuff.

Thanks for advice.
 
63A seems a bit hefty for a garage supply…. Is it just “sockets and lights” or is there some heavy duty workshop, sauna or hot tub out there?

Some entire houses are only 60A

Same with the 10mm extension…. That can carry about 50A just on its own.

Ok… if it’s used as an office, there might be a couple computers and monitors.. printer? Plug in heater for the colder days?

The length of cable run can make a difference… any idea how long the existing 16mm is, and then the proposed extra bit?
 
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a 16mm 3 core swa and is fused at 63amps with rcbo feeding sockets lights etc.
I have now built a cabin further down the garden and want to provide another CU in it for sockets and lights. It will be an outside office. I can’t run a feed back to the house so my question is can I take an additional feed of off the garden CU into the cabin and have another CU there. If so what would be the Fuse Isolator rating for the new CU in the cabin. I do have enough 10mm 3 core swa to run to the cabin. Assume no heavy loads on Garden or Cabin as it’s all low power stuff.

Thanks for advice.
You could just use a spare way (If you have one) off the garage sub main with a 40 amp mcb
 
63A seems a bit hefty for a garage supply…. Is it just “sockets and lights” or is there some heavy duty workshop, sauna or hot tub out there?

Some entire houses are only 60A

Same with the 10mm extension…. That can carry about 50A just on its own.

Ok… if it’s used as an office, there might be a couple computers and monitors.. printer? Plug in heater for the colder days?

The length of cable run can make a difference… any idea how long the existing 16mm is, and then the proposed extra bit?
The 16mm is 20 meters from the henley block and run to the cabin will be 10 meters.
 
63A seems a bit hefty for a garage supply…. Is it just “sockets and lights” or is there some heavy duty workshop, sauna or hot tub out there?

Some entire houses are only 60A

Same with the 10mm extension…. That can carry about 50A just on its own.

Ok… if it’s used as an office, there might be a couple computers and monitors.. printer? Plug in heater for the colder days?

The length of cable run can make a difference… any idea how long the existing 16mm is, and then the proposed extra bit?
The garden supply will have a 7kw sauna at a later date which has the 16mm swa 3 core to it
63A seems a bit hefty for a garage supply…. Is it just “sockets and lights” or is there some heavy duty workshop, sauna or hot tub out there?

Some entire houses are only 60A

Same with the 10mm extension…. That can carry about 50A just on its own.

Ok… if it’s used as an office, there might be a couple computers and monitors.. printer? Plug in heater for the colder days?

The length of cable run can make a difference… any idea how long the existing 16mm is, and then the proposed extra bit?
 

Attachments

  • cabin cu.jpg
    cabin cu.jpg
    233.5 KB · Views: 72

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Wood Cabin Consumer Unit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Bedders,
Last reply from
Bedders,
Replies
4
Views
1,617

Advert