Already stated that calcs have been done by 'others' and I'm struggling to see why I need to a adiabatic on a fly lead.
Discuss Earthing inside a submain panel from main swa incomer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Already stated that calcs have been done by 'others' and I'm struggling to see why I need to a adiabatic on a fly lead.
Already stated that calcs have been done by 'others' and I'm struggling to see why I need to a adiabatic on a fly lead.
The opposite is what I meant, the resolution of most meters will be to 2 decimal places 0.01, because he is so close to the TX the meter will struggle to verify such a low reading as it will need a minimum level of resistance to settle the reading, as the expected reading is probably going to be at the meters threshhold then it will not find its reading correctly and will generate false readings which will confuse anyone taking them. There are a few options to counter this, buy a nice expensive meter with a higher resolution, or introduce a known resistance into the reading. A simple way would be a local radial socket/spur etc where you can measure the cables R1+R2 giving you a known resistance then you can measure the external impedance from that socket minus the circuits impedance this will then bring your meter back to an accurate reading within its resolution. A simple resistor with high accuracy will also do the trick but not many carry these about as a rule.I dont think he is doubting you are not going to test,I believe what he is saying ,is the test equipment may max out at possibly 20 KA and you may not get an accurate reading
Sorry haven't read the whole post as just walked in the door and the Misses is moaning! Lol
Doesn't GN8 cover what SWA armour can be used as a CPC and which need additional bonding (therfore in parallel).
I'm not sure if I'm allowed to post a link to the page I'm referring to, so please let me know if this is permitted - Mods not us minions! Lol
This still will not answer my OP.
FYI the supply cable is FP600, so please post the relevant docs.
Reg 543.2.7...where the protective conductor is formed by metal conduit, trunking or ducting or the metal sheath and/or armour of a cable, the earthing terminal of each accessory shall be connected by a separate protective conductor to an earthing terminal incorporated in the associated box or other enclosure.
Not too sure this reg' actually covers the OP's situation, the main switchgear and or distribution equipment isn't classed as an accessory like equipment tapped of each circuit would be IMHO, I did think of this reg' myself but decided it wasn't for this situe'.
How come you wouldn't class it as the same situation?
I was referring to GN8 Appendix B (page 161)
This still will not answer my OP.
FYI the supply cable is FP600, so please post the relevant docs.
Reply to Earthing inside a submain panel from main swa incomer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net