Could This Be A Fused Neutral? | Page 3 | on ElectriciansForums

Discuss Could This Be A Fused Neutral? in the UK Electrical Forum area at ElectriciansForums.net

S

SparkyMcsparkface

Hi, came across this today, double width cutout, never seen it before. Not sure if it could be fused on the neutral or whether I am worrying with no need. Any advice appreciated. (Haven't pulled the cutout obviously, even though it isn't sealed - I have a feeling it might be too stiff to pull out anyway, maybe....)

[ElectriciansForums.net] Could This Be A Fused Neutral?
 
I wish to state that I agree with the use of the FI (Further Investigation required) code for apparent deficiencies with the DNO's equipment. In principle if fused neutrals were suspected (without getting in to whether this was a reasonable belief or otherwise) then the DNO are needed to verify this, and so further investigation without delay is required. It is also clear that this must result in an Unsatisfactory report.
 
That's interesting to know Dave. Is that an across the UK thing or just SSE? Also are meters currently meant to be checked every two years? The reason I ask the last bit is I see a lot of meters with poorly installed tails with exposed inner insulation and sometimes slightly exposed conductors at the terminals. I know the logistics of planning to update where necessary must be a nightmare at times, and cannot see how each and every install would actually be checked every two years. Is it not also dependant on whether the meter reader is diligent enough to report all they see that should be updated? I suspect many can't be bothered too!

Edit: I just noticed that you used the word "still" above.
Yes that is across all suppliers, and yes an answer to your question we do rely on DR's to pick this up if they can be bothered.
 
I wish to state that I agree with the use of the FI (Further Investigation required) code for apparent deficiencies with the DNO's equipment. In principle if fused neutrals were suspected (without getting in to whether this was a reasonable belief or otherwise) then the DNO are needed to verify this, and so further investigation without delay is required. It is also clear that this must result in an Unsatisfactory report.
Fused neutrals are being replaced by the DNO, but they are Cat B, when identified.
 
As a matter of interest what is Cat B defined as.
Westie in other words it is not classed as CAT A, exposed live parts, where they have to respond within 3hrs, I think the lead time for CATB is 2 weeks, CAT C , is when they can get there, eg broken tag on the cut out or fuse carrier.
 
Fused neutrals are being replaced by the DNO, but they are Cat B, when identified.
That may be, but the Electrician (in my view) was absolutely right to state that Further Investigation was required (in this case by the DNO). It is also clear that we then have no option but to assess the overall condition of the electrical installation as "Unsatisfactory". As such I feel that the criticism of the Electrician in this instance is grossly unfair as he acted appropriately.
 
Westie in other words it is not classed as CAT A, exposed live parts, where they have to respond within 3hrs, I think the lead time for CATB is 2 weeks, CAT C , is when they can get there, eg broken tag on the cut out or fuse carrier.

The service levels on cat b are 8 weeks I believe, but the fused neutrals must be done within 28 working days as required by the hse.
 

Reply to Could This Be A Fused Neutral? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
No and why are they not earthed??? Presumably there's no CPC in the cable?
    • Like
Replies
10
Views
2K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
489
  • Question
Maybe you could get the cut-out replaced and upgraded to PME. If so, Then you could turn it around to face to the outside wall and move the...
Replies
21
Views
3K
  • Question
Thanks indeed, Lucien, RE THE ABOVE If each coil has one of the three phase connected to it, and a delta configuration has only three supply...
2
Replies
25
Views
7K
  • Question
Ok Dave thanks, no more accidents yet 🙏😂….
    • Like
    • Informative
    • Winner
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks