I wish to state that I agree with the use of the FI (Further Investigation required) code for apparent deficiencies with the DNO's equipment. In principle if fused neutrals were suspected (without getting in to whether this was a reasonable belief or otherwise) then the DNO are needed to verify this, and so further investigation without delay is required. It is also clear that this must result in an Unsatisfactory report.
 
That's interesting to know Dave. Is that an across the UK thing or just SSE? Also are meters currently meant to be checked every two years? The reason I ask the last bit is I see a lot of meters with poorly installed tails with exposed inner insulation and sometimes slightly exposed conductors at the terminals. I know the logistics of planning to update where necessary must be a nightmare at times, and cannot see how each and every install would actually be checked every two years. Is it not also dependant on whether the meter reader is diligent enough to report all they see that should be updated? I suspect many can't be bothered too!

Edit: I just noticed that you used the word "still" above.
Yes that is across all suppliers, and yes an answer to your question we do rely on DR's to pick this up if they can be bothered.
 
Under ESQCR all neutral fuses were to be replaced with a solid link by 2013. I would think its highly unlikely there is a neutral fuse in there.
 
I wish to state that I agree with the use of the FI (Further Investigation required) code for apparent deficiencies with the DNO's equipment. In principle if fused neutrals were suspected (without getting in to whether this was a reasonable belief or otherwise) then the DNO are needed to verify this, and so further investigation without delay is required. It is also clear that this must result in an Unsatisfactory report.
Fused neutrals are being replaced by the DNO, but they are Cat B, when identified.
 
Fused neutrals are being replaced by the DNO, but they are Cat B, when identified.
That may be, but the Electrician (in my view) was absolutely right to state that Further Investigation was required (in this case by the DNO). It is also clear that we then have no option but to assess the overall condition of the electrical installation as "Unsatisfactory". As such I feel that the criticism of the Electrician in this instance is grossly unfair as he acted appropriately.
 

Reply to Could This Be A Fused Neutral? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all. I have a question i'm hoping some of you can advise on. A long story short my main fuse has been hidden in the wall cavity(by the previous...
Replies
21
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top