Morning all, i plan on extending ring circuit, installing additional 13A socket in the room.

Plan of action was to install black 30A junction box under floorboard to one of the legs. However after some research on this forum, junction box must be easily accessible and not suitable for the job. I'm not too sure if i will either go with carpet or permanent laminate flooring.

What would you guys suggest, 3 wagos inside existing backbox and extending from that

Or

Wago box under floorboard

Or blue crimps again inside the boxbox.

Thank you in advance.
 
wagos in existing socket box for me. if only 1 socket added, no need for FCU. unless you don't want to chase decor. in that case a MF box under floor.
 
Morning all, i plan on extending ring circuit, installing additional 13A socket in the room.

Plan of action was to install black 30A junction box under floorboard to one of the legs. However after some research on this forum, junction box must be easily accessible and not suitable for the job. I'm not too sure if i will either go with carpet or permanent laminate flooring.

What would you guys suggest, 3 wagos inside existing backbox and extending from that

Or

Wago box under floorboard

Or blue crimps again inside the boxbox.

Thank you in advance.

Why not extend the circuit from the sockets themselves? Removing the need for any junction boxes.
 
Screwfix have gaping holes in their catalogue .........
Must have been a glitch somewhere then Mate, when I worked for them the stock control was very good.
The OP intends extending the ring, not spuring off from the ring.
I would use crimps in the back box.
If the OP spurred from the nearest socket outlet, then he wouldn't need to crimp anything!
 
Ok, I must have my thick head on today.
Why, if you can get to the back box of the socket not just extend from the socket itself?

First time doing this...spurred of before but im a heavy user. I could use heaters which are power hungry. Also i run alot of computer equipment for work purposes 24/7. i think it would be better suited to extend ring given that it would take same amount of work.
 
I think I'll go with crimp, finally unpack my brand new crimper

Plus I'm a cheapskate.

If they are the standard red/blue/yellow crimps, they are not designed for use on solid conductors and do not provide any guarantee of a good, long lasting connection.

For solid cores you should be using uninsulated indent crimps and then the necessary good quality heatshrink sleeving to insulate them.

For extending rings in back boxes I find the Ideal in-line splices are fantastic...

https://www.NoLinkingToThis/p/ideal-spliceline-in-line-wire-connectors-pack-of-10/42201
 
It’s not stock control, it’s whats on the shelf in the local stores ...... not in the central stores
Stock control in the Screwfix outlets are controlled, updated on a daily basis, from personal experience, I can vouch for their product maintainability.
 
If they are the standard red/blue/yellow crimps, they are not designed for use on solid conductors and do not provide any guarantee of a good, long lasting connection.

For solid cores you should be using uninsulated indent crimps and then the necessary good quality heatshrink sleeving to insulate them.

For extending rings in back boxes I find the Ideal in-line splices are fantastic...

https://www.NoLinkingToThis/p/ideal-spliceline-in-line-wire-connectors-pack-of-10/42201

https://www.NoLinkingToThis/p/ideal-in-sure-2-port-push-in-wire-connectors-pack-of-100/50427

Are these any good?
Or these...

https://www.NoLinkingToThis/p/ideal-in-sure-3-port-push-in-wire-connectors-pack-of-100/56118
 
Last time I checked, there were many crimp manufacturers that state their crimps are suitable for solid conductors.

I wouldn't use them due to the nature of the crimp construction. As you know, typically they are a split tube which is simply pressed into an oval shape when crimped. Usually it's quite a thin wall on the tube and I'm just not convinced they stand up well to the thermal cycling they may experience.

I've certainly tried a variety of crimps on solid cable in the past and not had much joy (various crimp manufacturers and various crimp tools), and I've pulled far too many apart with very little effort that have been installed on sites I've worked on, so I just steer clear and use things like the SpliceLine and Wagos.
 
https://www.NoLinkingToThis/p/ideal-in-sure-2-port-push-in-wire-connectors-pack-of-100/50427

Are these any good?
Or these...

https://www.NoLinkingToThis/p/ideal-in-sure-3-port-push-in-wire-connectors-pack-of-100/56118

They are Ideals Wago and will do the job. I find the SpliceLines are easier to secrete in the backbox, particularly if it's a bit tight.
 

Reply to Extending ring circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock