I have come to extend a ring main on the old wiring (red and black) and have used the wago 222 connectors to extend each leg and extended each leg in a wago junction box and are all connected in the ceiling screwed to joists. The wago 222’s are rated at 32A but when used maintenance free like I have they’re de rated to 20A. The ring is on 32A RCBO, will it be safe with each leg extended with the 222’s even as they’re derated to 20A because they’re in a MF box in the ceiling? Thanks
 
Welcome to the forum mate.
You will be ok with using 222 for extending ring circuits.
If you are concerned about it you could always swap them for 773 connectors, that are rated at 32A when in the wago boxes.

Edit: You should also have RCD protection for the circuit.
 
Last edited:
Welcome to the forum mate.
You will be ok with using 222 for extending ring circuits.
If you are concerned about it you could always swap them for 773 connectors, that are rated at 32A when in the wago boxes.

Edit: You should also have RCD protection for the circuit.
Thanks appreciate it! What makes them alright to use to extend a ring is it just that each leg doesn’t car 32A so it is not needed to have one rated at that ?
 
Thanks appreciate it! What makes them alright to use to extend a ring is it just that each leg doesn’t car 32A so it is not needed to have one rated at that ?

Pretty much so.
Does the circuit have RCD protection?
 
Thanks appreciate it! What makes them alright to use to extend a ring is it just that each leg doesn’t car 32A so it is not needed to have one rated at that ?
The only reg for ring final circuits talks about the current carrying capacity of the cable being not less than 20 amps, and the load current in any part of the circuit not exceeding the cable's capacity for any long periods (paraphrasing wildly).

In other words, 20A is in fact the minimum rating. (see reg 433.1.204 for the whole delightful text)
 
Just make sure you use a wago box for each leg and not have all four legs in one box as per wago's instructions

I'm interested in where this nugget is too.

The maintenance free instructions for Wagobox clearly instruct you to reduce the maximum current for the terminals and also the maximum aggregate current which they state is the number of phase conductors * OCPD rating but they also say there are some situations where this may not be the case. I've taken that to suggest that as the maximum current in an RFC is limited to 32A it's within the 50A aggregate limit and therefore it's acceptable to put both joins in one box.
 
I'm interested in where this nugget is too.

The maintenance free instructions for Wagobox clearly instruct you to reduce the maximum current for the terminals and also the maximum aggregate current which they state is the number of phase conductors * OCPD rating but they also say there are some situations where this may not be the case. I've taken that to suggest that as the maximum current in an RFC is limited to 32A it's within the 50A aggregate limit and therefore it's acceptable to put both joins in one box.
If you watch this and then do the calculations a 32a supply will take it well over the 50a aggregate
 
Where is the pic with 4 legs going into box? Again watch the vid and do the calc.

It's not in the video... I was commenting about the documentation by Connexbox....

1666706403934.png
 
Just make sure you use a wago box for each leg and not have all four legs in one box as per wago's instructions
My bad......Think i wrote this and confused things...What i mean is a Wago box for each leg of the ring ( 2 cables) as per wago's instructions. Not both legs meaning 4 cables in the same box
 
My bad......Think i wrote this and confused things...What i mean is a Wago box for each leg of the ring ( 2 cables) as per wago's instructions. Not both legs meaning 4 cables in the same box

Ahhhh :)

Can't even imagine trying to pull that off with a standard Wagobox :D
 

Reply to Extending ring main with wago 222 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Replies
7
Views
1K
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
Hi all, I’ve had some good advice here in the last week or so which has made me ask a few more questions. 1. Ring main uses the old Red and Black...
Replies
10
Views
2K
Hi all, I’m after some advice regarding use of Wago boxes for adding a spur off a ring final. Is it okay to use a MF Wagobox with 221 Wago...
Replies
10
Views
3K
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock