I have come to extend a ring main on the old wiring (red and black) and have used the wago 222 connectors to extend each leg and extended each leg in a wago junction box and are all connected in the ceiling screwed to joists. The wago 222’s are rated at 32A but when used maintenance free like I have they’re de rated to 20A. The ring is on 32A RCBO, will it be safe with each leg extended with the 222’s even as they’re derated to 20A because they’re in a MF box in the ceiling? Thanks
 
Welcome to the forum mate.
You will be ok with using 222 for extending ring circuits.
If you are concerned about it you could always swap them for 773 connectors, that are rated at 32A when in the wago boxes.

Edit: You should also have RCD protection for the circuit.
 
Last edited:
  • Like
Reactions: BenCos18
Welcome to the forum mate.
You will be ok with using 222 for extending ring circuits.
If you are concerned about it you could always swap them for 773 connectors, that are rated at 32A when in the wago boxes.

Edit: You should also have RCD protection for the circuit.
Thanks appreciate it! What makes them alright to use to extend a ring is it just that each leg doesn’t car 32A so it is not needed to have one rated at that ?
 
Thanks appreciate it! What makes them alright to use to extend a ring is it just that each leg doesn’t car 32A so it is not needed to have one rated at that ?

Pretty much so.
Does the circuit have RCD protection?
 
  • Like
Reactions: timhoward
Thanks appreciate it! What makes them alright to use to extend a ring is it just that each leg doesn’t car 32A so it is not needed to have one rated at that ?
The only reg for ring final circuits talks about the current carrying capacity of the cable being not less than 20 amps, and the load current in any part of the circuit not exceeding the cable's capacity for any long periods (paraphrasing wildly).

In other words, 20A is in fact the minimum rating. (see reg 433.1.204 for the whole delightful text)
 
  • Like
Reactions: Spoon
Just make sure you use a wago box for each leg and not have all four legs in one box as per wago's instructions
 
Yeah it is on a RCBO thanks 🙂
 
  • Like
Reactions: DPG
Just make sure you use a wago box for each leg and not have all four legs in one box as per wago's instructions
Is that an actual regulation or just because it’s too much of a squeeze?

I’ve extended rfc with a joint in back of socket box. Same thing, isn’t it?
 
  • Like
Reactions: SparkyChick
Just make sure you use a wago box for each leg and not have all four legs in one box as per wago's instructions

I'm interested in where this nugget is too.

The maintenance free instructions for Wagobox clearly instruct you to reduce the maximum current for the terminals and also the maximum aggregate current which they state is the number of phase conductors * OCPD rating but they also say there are some situations where this may not be the case. I've taken that to suggest that as the maximum current in an RFC is limited to 32A it's within the 50A aggregate limit and therefore it's acceptable to put both joins in one box.
 
  • Like
Reactions: Spoon and loz2754
I'm interested in where this nugget is too.

The maintenance free instructions for Wagobox clearly instruct you to reduce the maximum current for the terminals and also the maximum aggregate current which they state is the number of phase conductors * OCPD rating but they also say there are some situations where this may not be the case. I've taken that to suggest that as the maximum current in an RFC is limited to 32A it's within the 50A aggregate limit and therefore it's acceptable to put both joins in one box.
If you watch this and then do the calculations a 32a supply will take it well over the 50a aggregate
 
  • Like
Reactions: SparkyChick
Interesting this actually shows a ring main extension in the use cases :)
Where is the pic with 4 legs going into box? Again watch the vid and do the calc.
 
Where is the pic with 4 legs going into box? Again watch the vid and do the calc.

It's not in the video... I was commenting about the documentation by Connexbox....

1666706403934.png
 
Just make sure you use a wago box for each leg and not have all four legs in one box as per wago's instructions
My bad......Think i wrote this and confused things...What i mean is a Wago box for each leg of the ring ( 2 cables) as per wago's instructions. Not both legs meaning 4 cables in the same box
 
  • Disagree
Reactions: Petej999
My bad......Think i wrote this and confused things...What i mean is a Wago box for each leg of the ring ( 2 cables) as per wago's instructions. Not both legs meaning 4 cables in the same box

Ahhhh :)

Can't even imagine trying to pull that off with a standard Wagobox :D
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
United Kingdom
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Extending ring main with wago 222
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Dvyj123,
Last reply from
SparkyChick,
Replies
15
Views
5,926

Advert