I suppose if you have an understanding of power tools then it’s fine one of my best mates does it with impact and I cringe every time I see/hear him at the consumer but to be fair he understands the torque it’s the ones who don’t have knowledge/experience that cause the problems anyhow I don’t like power tools at consumer
The drill/driver is used in that video is not an impact driver and can be set to exceptionally low torques. I've no idea what it was set at and whether or not those terminals were over/under tightened, but it's worth noting that they are very different tools.
Doesn’t matter shudn be using them unless like @telectrix just posted then that’s the exception “HAND TOOLS ONLY”
Drill drivers can be set to exceptionally low torques - often so low that it wouldn't be considered much more than hand tight.
Having said that, I just looked at the video again and note that it is indeed an impact driver :tearsofjoy:
What
what do you use mate? Drill/driver is it?
[automerge]1601669683[/automerge]
I don't regularly fit consumer units - in fact I've fitted a grand total of one and the use of power tools was limited to mounting it.
If people are using 18v impact drivers to tighten down terminal screws something went wrong with the trade...
I'll be honest if I've got a board full I'll wizz all the terminals fully open with the driver and tighten them back up just tight enough to hold then run down the lot with the torque driver.
If you use an impact enough then you can be quite gentle with it.
Never rounded a screw yet
Ok so you’re under the category of experienced but I’m sure you agree with the fact that it’s more sensible to hand tighten terminations so you can feel the tension
[automerge]1601670108[/automerge]
Good man stick to the hand tools once mounted ?
Reactions: DPG and nicebutdim
There's a time and a place, if its an obsolete MCCB it'll be hand tools only, if its a board change and mistakes can rectified the returns outweigh the risk.
What does grind my gears is certain manufacturers applying thread lock to terminal screws, not sure how that helps come EICR time.
I don't know how these manufacturers calibrate their torque screwdrivers, but mine was so far out it could not be tightened to 2.1N required by Hager without bending the Din rail the RCBO was fixed too, anyone want to buy a full set of Armeg drivers?
Normally it’s 1.7N isn’t it? Only 2.1 or higher for main switch you don’t need torque settings to know the correct torque I don’t think aslong as you understand the recommendations
[automerge]1601671339[/automerge]
Difficult area but again like I said it all boils down to experience and knowledge
None of Hagar's equipment is recommended to be torqued to as low as 1.7N, in fact it can be as high as 3.6N.
It would depend on the type of threadlock.
Some is soft and easy to undo, only to stop gross loosening from vibration, etc. But some (e.g. "studlock") is like superglue and never expected to be undone without serious force!
If you do need to stop an adjuster from moving unintentionally and don't have anything special to hand you can use a dab of nail varnish, which you can get pretty much in any local chemist or supermarket.
Reactions: telectrix
i have a small bottle of Loktite on the van. still half full after 20 years of occasiona luse.
It's a good excuse for why you're carrying nail varnish as well. I always carry women's tights as well in case my fan belt breaks.
In case there are any woke snowflakes reading this... I should add that mens tights would work just as well.
You should connect the cpcs first.
So when you test N-E for a particular circuit you will have all the CPC's connected in the earth bar? What would be wrong with doing the IR testing of N-E without having the CPC's in the earth bar? Are you saying parallel paths could cause different results? Are we not testing that particular circuit, i.e that particular cable, which is why we put the test result in the little box related to that one circuit?
A lot of questions there!
Reactions: Dave OCD
There could be Parallel paths to earth. I’ve never know anyone to not IR test with everything connected to the MET
Reactions: westward10
See Regulation 643.3.1
The CPC of the circuit being tested is probably isolated from all the others CPCs and the Earth, so you would not see a leak from N to true Earth (e.g. a screw, etc, that is touching the N copper and in to plasterboard, etc) as it would not be guaranteed to complete the circuit from true Earth to CPC and back to your IR tester.
[automerge]1601722401[/automerge]
Basic idea is this (sorry for poor diagram):
[automerge]1601722565[/automerge]
So IR testing with the CPC isolated will pick up on an internal cable fault (say N to E), but not for external faults (N to some other CPC or true Earth).
Interesting - is that there to increase safety during the test and avoid 500V appearing on random metalwork for any length of time? Or is it to detect and test any parallel paths?
Interesting, I'd never really appreciated that. Though a screw piercing only N through plasterboard, would not be detected in any case would it? What would the viable parth to earth be for a screw, assuming it wasn't into a metal stud or in very wet plaster at time of test?
I guess it would pick up where the neutral for one circuit was damaged where it passed through the backbox of a different circuit or where rodent damage allowed the exposed neutral of a lighting circuit to touch cpc of a power circuit running alongside it in the loft.
I'll admit I've sometimes done the IR after first fix, mostly to check that plasterers haven't damaged a cable, and then not rechecked once connected.
On EICRS I usually do them with the cpcs connected, if only because it is sometimes hard to be sure which one is which anyway in a poorly installed board. (Though RFCs have to be located anyway of course)
[automerge]1601724182[/automerge]
Just to add, I'm fairly sure on previous NICEIC inspections when they check my testing procedure (Usually a RFC continuity test, R1+R2 and then IR) they have never mentioned replacing the cpc before testing.
Obviously it's more to see the procedure than to actually do the test at that point, but maybe I'll get brownie points for ensuring I do at the next one - or he'll ask what I'm doing that for! ;)
south west
Consumer unit change - How do you do it?
catdog1121,
stevethesparks,
